Discuss Testing continuity with downlighters in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

J

johntom

Hi
just wanted to check something with you guys.
If you tested R1 + R2 on seperate a 6a lighting circuit with just selv downlighters (using a temp link in the cu), where would you take the reading from ?
 
Same as always at the furthest point.

If there are many downlights throughout the building i expect the circuits will be terminated at the switches, which would make things a little easier.

Good luck!
 
Hi
yes because of the transformers, presumably you would you have to test at the end of the T&E (instead of the normal cpc / switch live inside the ceiling rose) otherwise no cpc / R2 in the downlighter fitting from the transformer?
 
hi i always test at the last light ( furthest point ) there is nothing wrong in testing at the switch
in the new gn3 it shows ( R1+R2) being taken from the switch
 
Testing at the last point is fine, if you only have single points in each room, But when you come to Spots you need to prove that each Spot circuit has earth to the end of its run, So in effect, test at the very last point of the circuit, but if another room has downlighters in you should also test at the last point in that downlight set up. Doe's that make sense??


Im effect when fitting downlighter in multiple rooms Your Spurring off a Radial circuit, So CPC should be checked at the end of each 'spur'.
 
Hi
do you test the end of the T&E as there wouldn't be a cpc from the transformer to the downlighters (so you can't test R2 by removing the bulbs) ?
 

Reply to Testing continuity with downlighters in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi I have an electrician over and he took over from an incompetent builder. The builder already installed the wiring but the electrician told me...
Replies
22
Views
916
  • Article
Electrical2Go - Mega Downlight Deal - Don't miss out! Taking place from August 18th to 20th, we're offering an incredible promotion for...
Replies
1
Views
621
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
846
I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...
Replies
5
Views
614
Hi all. Reasonably competant non electrical engineer homeowner here. I have a question for the experts: I recently replaced a horrible...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock