Discuss Testing Emergency lighting circuits in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
I have just started installing temporary emergency lights for a fire alarm company i work for i am an electrician qualified to the 18th edition i do not currently do testing and inspection looking at doing this in a few months. Just looking for some advice and information about the testing of emergency lighting circuits once it is installed as i do not normally install emergency lighting.

I have installed 5 emergency LED bulkheads which comes from a key switch, the feed comes from the DB which is connected into the rcbo of the circuit feeding the normal lights so when it trips the lights will come on.

Can some one explain to me which test would have go to be carried out to ensure no damage to the LEDs

I have tried to ask another electrician that's doing to testing but not interested in explaining it to me
 
You test it like any other circuit. You either insulation resistance test between line and neutral before the fittings are connected then earth or you just connect line and neutral together and just test to earth if the fittings are connected, it won't damage them.
 
Aside from that you want to see the charging LED is functional when power is on and when off the charging light goes out and the emergency light comes on. As you have to wait at least 24 hours for the batteries to be fully charged you cannot practically do the three hour test. There is usually a schedule of tests to fill in with each emergency light as well. The date needs to be put on the battery as to when it was commissioned. But having done the functional tests that is it. There are requirements for 1 lux to hit the floor they are illuminating at one meter wide. Usually, apart from a lux meter, calibrated, you would use the manufacturers information on the lumens delivered to assure you meet that requirement. Then of course you would ensure that they are installed correctly in the sense the design allow for changes of direction and levels etc. according to BS5266
 
Get a copy of 5266-1 or have the company provide you with it as you'd do the standard electrical tests but there may also be (dependant on system) specific tests required by 5266-1.
 

Reply to Testing Emergency lighting circuits in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi Guys I've fitted a few emergency lighting circuits to both domestic and commercial installs before, I've come across one I can't get my head...
Replies
19
Views
1K
Hi I'm in need of some advice. First of all i'm not an electrician but do have an understanding of electrics as i come from an electronics...
Replies
4
Views
627
Hi folks, Can anyone recommend a reliable brand for emergency lighting bulkheads please? I have a job coming up to replace 30 odd units. I have...
Replies
2
Views
467
Hi guys, Been asked to fit 2 lights and a switch, which in reality turned out to be rewiring a multiple PIR setup to a single switch, adding...
Replies
0
Views
843
Hi, RCBO appropriate test facility for emergency lighting? I have a car storage facility ( one corridor with 10 rooms off the corridor to store...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock