Part of the testing is to verify an existing design is in place and that it is current.
Sorry, that would be initial verification.
Monthly or annual testing, battery duration testing and functional testing do not require verification of design.
Any alterations which could affect the existing design, such as new walls, different colour scheme, etc, should result in a revised design at the time of the alteration.
 
I would estimate 99% of emergency lighting installations I test or assess for FRAs are not and have never been compliant with not only current but the standards they should have been installed to at the time, you can also include fire alarm systems to this. I find it bewildering that people berate those who undertake electrical work without a sound underpinning of the requirements and yet will happily install safety systems with the same ignorance.
 
Monthly or annual testing, battery duration testing and functional testing do not require verification of design.

Annex K of BS5266:1 provides a Certificate for this exact purpose.
 
I would estimate 99% of emergency lighting installations I test or assess for FRAs are not and have never been compliant with not only current but the standards they should have been installed to at the time, you can also include fire alarm systems to this. I find it bewildering that people berate those who undertake electrical work without a sound underpinning of the requirements and yet will happily install safety systems with the same ignorance.
In many instances, the installer is installing to a design supplied by another.
Cables is cables whether it’s for power and lighting, emergency lighting or fire alarms.
Such installers don’t need to know the maximum height of a void above a ceiling before a smoke head has to be installed.
They don’t need to know whether the head should be heat or ionisation.
They don’t need to know the minimum distance from a wall, or from light fittings and other equipment.
They don’t need to know when an emergency exit sign should be maintained or non-maintained.

Yes knowing such things would be useful, but as long as they install as per the design, everything should be ticketyboo.
 
In many instances, the installer is installing to a design supplied by another.
Cables is cables whether it’s for power and lighting, emergency lighting or fire alarms.
Such installers don’t need to know the maximum height of a void above a ceiling before a smoke head has to be installed.
They don’t need to know whether the head should be heat or ionisation.
They don’t need to know the minimum distance from a wall, or from light fittings and other equipment.
They don’t need to know when an emergency exit sign should be maintained or non-maintained.

Yes knowing such things would be useful, but as long as they install as per the design, everything should be ticketyboo.
That may be the case but this does not change the fact a multitude of systems are not compliant. Assessing whether AFDs are required in voids can only be known if the Category of system is known. Minimum spacing from walls and luminaires is a basic requirement for any Category of system.
 
I would estimate 99% of emergency lighting installations I test or assess for FRAs are not and have never been compliant with not only current but the standards they should have been installed to at the time, you can also include fire alarm systems to this. I find it bewildering that people berate those who undertake electrical work without a sound underpinning of the requirements and yet will happily install safety systems with the same ignorance.
Perhaps, as you seem to be suggesting, nobody considered themselves sufficiently competent to upgrade it, so just left it alone.
 
If you are annual or monthly testing you do not need to verify the design. Comments should be noted on test certificate & log book. If the fire risk assesment deems it an unsatisfactory design then that will force the client to take action.
Annual test you are there to test that the battery withstands the 3hr test without the light fading. No new exits or walls are apparant and the general el install, i would always comment if no easily accesible key switch is readily available but wouldnt give an unsatisfactory if there wasnt one.
 

Reply to Testing emergency lighting in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi guys, Been asked to fit 2 lights and a switch, which in reality turned out to be rewiring a multiple PIR setup to a single switch, adding...
Replies
0
Views
657
Hi I'm in need of some advice. First of all i'm not an electrician but do have an understanding of electrics as i come from an electronics...
Replies
4
Views
658
Hello Got a customer who needs certification for a monthly emergency lighting test. What would be the best cert to provide them with? The NICEIC...
Replies
2
Views
475
I tested a self test emergency lighting with three gears .While testing 2 of the gear doesn't passed 3 hour test but 1 Did Wit the same battery ?Why?
Replies
6
Views
788
Hi Guys I've fitted a few emergency lighting circuits to both domestic and commercial installs before, I've come across one I can't get my head...
Replies
19
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock