Discuss Testing garage CU for assesment!!! in the UK Electrical Forum area at ElectriciansForums.net

Didnt opt to use PME from house, instead earth staked the outside building. Obviously a big no no from the sparks on here. Thanks

It’s not a big no no, it is sometimes necessary to do this, however in your installation it sounds like there were better options.

Unless your earth electrode has a stable Ra somewhere below 1ohm then you’d be better off having used the TNCS earth in my opinion.
How have you isolated the earth of the SWA at the load end of the cable? Which earthing system have you connected the armour of the SWA to?

Merely putting in an earth electrode at the shed end won’t prevent the RCD in the house from tripping. The neutral is still referenced to true earth at the substation so the RCD will see the imbalance from any earth fault or leakage. To achieve what you want you would need to install an isolating transformer and set up a TNS supply to the shed by referencing one leg of the output to earth.

This hasnt even touched on the subject of discrimination and why feeding a submain from an mcb is rarely the best practice.

I realise you only asked about testing, but all of the points raised should also come up during your NIC assessment
 
Didnt opt to use PME from house, instead earth staked the outside building. Obviously a big no no from the sparks on here. Thanks

It’s not a big no no, it is sometimes necessary to do this, however in your installation it sounds like there were better options.

Unless your earth electrode has a stable Ra somewhere below 1ohm then you’d be better off having used the TNCS earth in my opinion.
How have you isolated the earth of the SWA at the load end of the cable? Which earthing system have you connected the armour of the SWA to?

Merely putting in an earth electrode at the shed end won’t prevent the RCD in the house from tripping. The neutral is still referenced to true earth at the substation so the RCD will see the imbalance from any earth fault or leakage. To achieve what you want you would need to install an isolating transformer and set up a TNS supply to the shed by referencing one leg of the output to earth.

This hasnt even touched on the subject of discrimination and why feeding a submain from an mcb is rarely the best practice.

I realise you only asked about testing, but all of the points raised should also come up during your NIC assessment
 
Thanks for the constructive reply. And yes I realise it's all relevant. Been googling all morning and picked up a bit more knowledge that I didnt have. Gonna alter my design get rid of earth stake & export existing earth. Thanks


It’s not a big no no, it is sometimes necessary to do this, however in your installation it sounds like there were better options.

Unless your earth electrode has a stable Ra somewhere below 1ohm then you’d be better off having used the TNCS earth in my opinion.
How have you isolated the earth of the SWA at the load end of the cable? Which earthing system have you connected the armour of the SWA to?

Merely putting in an earth electrode at the shed end won’t prevent the RCD in the house from tripping. The neutral is still referenced to true earth at the substation so the RCD will see the imbalance from any earth fault or leakage. To achieve what you want you would need to install an isolating transformer and set up a TNS supply to the shed by referencing one leg of the output to earth.

This hasnt even touched on the subject of discrimination and why feeding a submain from an mcb is rarely the best practice.

I realise you only asked about testing, but all of the points raised should also come up during your NIC assessment
 
All I asked was advice about testing. Thanks

I suppose we could have told you how to test it and then ignored ALL the inherent issues with your design & installation.

So, you've taken some flack, quite rightly for a daft design and now you won't have to answer awkward questions from a NICEIC assessor!

Surely you should be greatful.

My only other comment is to use 3 core in the future ... and a switch fuse.
 
My only other comment is to use 3 core in the future ... and a switch fuse.
Absolutely

It is very difficult to get discrimination between two MCBs. Just look at the discrim tables, and you’ll see why.
Hopefully your assessor will understand that you are just starting out and will be kind.
Buy good coffee and a big pack of chocolate hobnobs.

Do let us know how it goes.
 
Can I ask why the OP is being recommended to not use a not RCD protected way in the house CU, with RCD CU in log cabin, presuming he uses the PME?
 
You lost me with that ... but I simply questioned why he would purposely have 2 x RCD's in series...
Sorry Murdoch, you've mentioned using a switch fuse (#36) and Davesparks said 'why feeding a submain from an mcb is rarely the best practice' (#33). I understand the use of a switch fuse feeding a distribution circuit for a domestic property CU, but for a small CU for a log cabin or garage etc?
 

Reply to Testing garage CU for assesment!!! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi Guys, hopefully someone will know the answer. Testing an install on a (domestic) PME system I have a garage consumer unit supplied from one of...
Replies
17
Views
2K
I've just picked one of these up on a famous auction site. The voltages, low and high resistance ranges all appear to be working fine but it's not...
Replies
7
Views
298
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
375
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
928
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock