Sorry Murdoch, you've mentioned using a switch fuse (#36) and Davesparks said 'why feeding a submain from an mcb is rarely the best practice' (#33). I understand the use of a switch fuse feeding a distribution circuit for a domestic property CU, but for a log cabin CU?

Why not.

If you read the OP, he thinks that making the cabin TT, any tripping will be internal to the cabin and not the house despite the submain being on a "shared" RCD.....

Its very difficult to get proper discrimination between MCB's so when a switch fuse can be used, its better all round.

Most people avoid this option because its far more expensive.
 
Sorry Murdoch, you've mentioned using a switch fuse (#36) and Davesparks said 'why feeding a submain from an mcb is rarely the best practice' (#33). I understand the use of a switch fuse feeding a distribution circuit for a domestic property CU, but for a small CU for a log cabin or garage etc?

For a small CU in a log cabin discrimination is less of an issue I agree, and the implications of a lack of discrimination are unlikely to be much.
However it is better, in my opinion, to design and install to the highest possible standard.

Also this particular installation appears to be being done especially to please an NIC assessor so following the book to the letter may be sensible.
 
Why not.

Its very difficult to get proper discrimination between MCB's so when a switch fuse can be used, its better all round.

Most people avoid this option because its far more expensive.

Thanks for that. I get the discrimination thing. But in most cases, I've seen garage CU's supplied from an mcb in main CU. Its recommended by various members on here as a default way of supply, when someone seeks advice on supplying garage, shed, office CU's etc. In reality, I can't see a customer being happy, with a switch fuse put along side their CU in the hallway, not withstanding it would be easier to achieve that sort after discrimination.
 
For a small CU in a log cabin discrimination is less of an issue I agree, and the implications of a lack of discrimination are unlikely to be much.
However it is better, in my opinion, to design and install to the highest possible standard.

Also this particular installation appears to be being done especially to please an NIC assessor so following the book to the letter may be sensible.

Just that most domestic designs would follow the MCB approach, I don't think the assessor would be too critical of such a design?
 
Just that most domestic designs would follow the MCB approach, I don't think the assessor would be too critical of such a design?

Critical no, but they should be asking about the different ways to do such an installation.

As I previously commented, cost is almost certainly the "driver" - metal clad switch fuses don't come cheap!
 
Critical no, but they should be asking about the different ways to do such an installation.

As I previously commented, cost is almost certainly the "driver" - metal clad switch fuses don't come cheap!


I'm thinking something like this in the hallway;
upload_2018-4-11_21-11-43.jpeg

Then adding this;

upload_2018-4-11_21-13-29.jpeg
 
I'm thinking something like this in the hallway;
View attachment 41732

Then adding this;

View attachment 41733
If there are already five CUs in the hallway one more switch fuse wont make a difference.o_O:):p

A fuse carrier in the CU (if they are available) would be a neater solution, but there are not many makes readily available. You may also then come up against different manufacturers in one CU!.
 

Reply to Testing garage CU for assesment!!! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi Guys, hopefully someone will know the answer. Testing an install on a (domestic) PME system I have a garage consumer unit supplied from one of...
Replies
17
Views
2K
I've just picked one of these up on a famous auction site. The voltages, low and high resistance ranges all appear to be working fine but it's not...
Replies
7
Views
293
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
356
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
911
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock