Discuss Testing help in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

J

James Sutton

HI All

Have just installed a new circuit to supply power to a control panel.

Have tested it all came back fine if i need to carry out a ZE test how can this be done because cannot isolate the main board so cannot disconnect the Main CPC from the MET

Also have only carrird out a ZS at the furthest point of my installation which is the Switched Fused Spur

Should i do a ZS and PFC at the dis board or is at the spur fine

All results are recorded on schedule of test results the Red NIC forms. EXCEPT on the top left of the form where its asks for ZS AND PFC


Thanks just need a little guidance :confused:

James
 
ask dno for ze or use max value which they will prob give you anywayand it will result in a overall higher zs but as long as it is less than corrected Bs7671 values then your good to go
 
Last edited by a moderator:
Took the Zs reading at the spur the furthest point on the circuit

@0.36 ohm

Will i need to take a Zs reading at the board and PFC

R1+R2 value was 0.14 ohm

and Insulation resistance @ 299M ohm

MCB is a D type

Thanks for ya help

James
 
your zs is taken at the furthest point - as you have done
pfc would prob be between l/n incoming (pscc) and l/ main earth(pefc) the higher being recorded.

unless you mean fault current for the circuit in which case its the same but taken from the circuits conductors ( i doubt this is what you require as most pfc readings taken from step 1 above.

and max ze will be 0.8 on tns or 0.35 on tncs
 
your zs is taken at the furthest point - as you have done
pfc would prob be between l/n incoming (pscc) and l/ main earth(pefc) the higher being recorded.

unless you mean fault current for the circuit in which case its the same but taken from the circuits conductors ( i doubt this is what you require as most pfc readings taken from step 1 above.

and max ze will be 0.8 on tns or 0.35 on tncs

On a 3-phase system is it correct that the PSCC is doubled?

Also could the Ze be worked out by Zs-(R1+R2)
 
>299M ohm using a megger 1552


Thanks lads for all ya help just abit un clear on a few things have to get everything spot on as this PDU supplies comms room racks/servers and theres no way i can turn this board off and if i were to trip anything i would have to walk the plank lol

Understand a little bit better have just passed my 2391 so still a getting used to it thanks for all ya help

Thanks James
 

Reply to Testing help in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...
Replies
5
Views
634
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
854
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
653
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
349
I've just picked one of these up on a famous auction site. The voltages, low and high resistance ranges all appear to be working fine but it's not...
Replies
7
Views
290

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock