The BEAMA RCD handbook does state in the section for testing by installer;

All tests must be performed with all loads disconnected using an
appropriate calibrated test instrument connected as close to the RCD as possible.

But thats not the same as testing on the RCD terminals.
 
Also I think some rcds / rcbos actually need short pieces of cable on the load side to get a reading.
That is a lot of faff when , As has been stated, you are testing the circuit to the accessory to check the functionality of the RCD part of the RCBO. Now a ramp test is different and would warrant disconnection.
 

Reply to Testing RCBO at Light Switch in the ElectriciansForums.net News and Updates area at ElectriciansForums.net

Similar Threads

Thinking a 240V AC relay activated by two independent light switches could be used to switch power to a shared inline extractor fan. The fan...
Replies
31
Views
1K
I have an issue with a home lighting circuit 6A RCBO provides power to 13 bulbs which randomly keeps tripping, when I say randomly it keeps...
Replies
8
Views
2K
Hi, I have a single light switch, wired like this.. the 2 wires in com, with a always live wire coming to the switch, and then wire going out to...
Replies
6
Views
675
I own two flats with a small common lobby. Although operable from both flats, the common lobby light appears to be wired to flat A's circuit...
Replies
2
Views
403
Hi, in my bedroom i had a 2 gang dimmer that powered 2 set of 3 spot lights and also had passthrough wires to other sockets. Im changing to just...
Replies
2
Views
229

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock