tbs1983

Hi guys, not really done any 110v work and not something we ever covered in detail in college.

A workshop with fixed 110v outlets was having trouble with a 110v appliance,
Upon voltage testing the outlet I got the following readings:

L-N - 57v
L-E - 0v
N-E - 57v

Are these readings what I should get? Im unsure as Ive always worked on the 230/400v principle that L-N and L-E should produce voltages and N-E be 0v so its throwing me a bit.

I understand the basic principle that 110v works on a centre tapped earth therefore combines the two 55v to create the 110v.

Any advice would be greatly appreciated.

p.s. other 110v appliances work fine from the outlet so were assuming its the appliance at fault but I'm curious as to the above.
 
.think you;ve measured wrong. L-L = 110V. each L -E =55V. there's no N on a 55-0-55 110V
 
Bit of a silly question but recently done some temp 110 lights for a site and I was always told a bulb won't strike with out a neutral but in a 110v system there is no neutral?

They Definitely don't cover enough 110v systems in college barely Learnt about them expect their used on building sites and it's centre taped to earth
 
a bulb requres a voltage across it. it can't differentiate between L-N, L-E or L-L. as long as thers a potential of sufficient magnitude ( e.g. 110V in this case)
 
if the light is wired conventionally, e.g. in a house, across L -N, then you're right. if the N is lost, then the lamp won't work. however ( and this has given guys belts) because there's no current flow, the volt drop across the lamp iz 0V, so you will get 240V on the N side of the lamp.
 
Thanks Tel, can't recall ever covering 110v in college in any detail and its taken 10 years to come across it in the real world.
 
Bit of a silly question but recently done some temp 110 lights for a site and I was always told a bulb won't strike with out a neutral but in a 110v system there is no neutral?

They Definitely don't cover enough 110v systems in college barely Learnt about them expect their used on building sites and it's centre taped to earth


Definatly be buggered on ships then as there is no neutral on 99% of them
 
Centre tapped safety transformers most 110v supplies rely on this for safety reasons, 57v-0v-57v as said before lamps require a voltage applied across the terminals. Got a feeling the Yanks derive their 220v this way although I couldn't be sure, 110v-0v-110v = 220v
 
Or cars, doesnt everything end in an earth?

I know on old ships they used to use the hull as the return path or so ive heard

The negative of the battery went onto the frame so you only needed positive cabling (At least on the old cars ive played with, dont know so much about modern vechs)
 
older cars were + earth. remember a couple .
Lots of old plant too,i've converted plenty years back,dynamos,reg. boxes,reversed ammeter etc, thinking behind it was corrosion related,apparently. Was actually driving an old Manitou stacker yesterday that i did nearly thirty summers back.....starting to sympathise with that bloke in "highlander"...
 

Reply to testing voltage on 110v systems in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
660
Hi, I would love some help understanding an issue I’m having on a 16mm SWA cable running from the CU in my house to the CU in the shed. I believe...
Replies
15
Views
2K
all currently working towards my 2391 c&g I&T . I know how to calculate v.d. but the mock test I found online seems a bit out of date or I'm...
Replies
2
Views
788
Hi folks. Im a RECI contractor based in Co Sligo, Ireland . I was doing erroneous testing on a domestic board which gave me readings between 90V-...
Replies
14
Views
2K
Hi guys, I have recently encountered that my circuit breaker for the upstairs lights keeps tripping. I flick it back on and immediately it trips...
Replies
7
Views
914

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock