Hi I'm new to the site this is my first post. I currently in the 3rd year of my apprentiship. I've been asked to do a job for a friend, he wants 2x double socket outlets installing in the back garden. I'll be putting them on a 4mm radial using swa cable on a 20a breaker and obviously ip rated sockets supplied from the house db from a spare way on the rcd side. My question is...after the installation do I need to test the whole installation or just the new circuit???


Thanks in advance.
 
I was gonna test the circuit I installed and also make sure the boning was the right size and was continuous. Do I need to do a zs on all other circuits??
 
In seriousness you are there mate. You have the correct answer. The only need to test the circuit you are installing. It has to fully comply so all bonding will also need to be in place before you can sign off. Also as Murdoch said this job will be notifiable.
 

Reply to Testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Had an enquiry where the installation (commercial) is relatively new and client has requested a condition report. Probably 80-100 circuits plus...
Replies
8
Views
1K
Morning all, We are looking at qualification requirements for inspection and testing to BS EN 60204, all of our work is past the main isolator of...
Replies
2
Views
710
Hi all EICR today on a ground floor flat .. 1 issue .. At the consumer unit there was a 1mm core with its yellow (sleeved brown) in a 20A radial...
Replies
20
Views
2K
NICEIC Certification Scheme New Circuit - NO RCDs
A client wants an outdoor socket installing on a new circuit. The current installation doesn't have any RCDs for the other circuits. I would put...
Replies
4
Views
980
Opinions on this Crabtree TP 10 way board? Got to test this next week after a quick recce on a clients site yesterday. Although probably...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock