Is the whole electric gate installation business a subtle scam. Had gate installed with Thalia P controller and BFT electrics. Got my head around wireless remotes fairly quickly and sorted those out. However, the damn thing screws up every time there is a power cut. The Thalia user manual is deliberately vague and uses it's own codes which need an Einstein to work through so DIY is a nono and every power cut costs me a ÂŁ100 visit from the installer with his decryption gizmo which is much like the car servicing scam where you have to take your car to a main agent with the electronics to diagnose your problem with massive fees to update your software when they feel like it. When I buy something I expect to be given the means to maintain it. Gates people ensure you don't and the whole blasted industry is in league with them. Is this protectionism actually legal?
 
If it screws up every time power is switched off then there is something wrong and I would be getting them to fix it properly. Completely unsatisfactory.
 
I am wondering if you have a case for complaint against the installer.

They have provided a system that is not suitable for the environment it is installed in.
Keep a good record of all service call outs and what they say they have fixed.
if you have several "reset controller after power cut " then i would be pushing for it not being suitable for future use as it is unable to deal with something that is likely to happen regularly.
 
coventry (midlands, uk)

and some more words to help me post it.
 
are you able to replicate the fault at will?
i.e. if you turn off the main breaker to the building, leave it for 30 seconds and turn it back on does the problem appear again?
 
If it screws up every time power is switched off then there is something wrong and I would be getting them to fix it properly. Completely unsatisfactory.
Seems power cuts are a universal cause of gate problems. Wouldn't show me how to do it myself as it was 'too dangerous'. It's a 24v system with buttons designed to be pressed.
 
Seems power cuts are a universal cause of gate problems. Wouldn't show me how to do it myself as it was 'too dangerous'. It's a 24v system with buttons designed to be pressed.

It's not fit for purpose. No way would I be booking an engineer and having to be at home every time. And then getting charged ÂŁ100 for the privilege!
 
@meditek ,

What codes are you getting from the control board?
Good point. I'll check.
are you able to replicate the fault at will?
i.e. if you turn off the main breaker to the building, leave it for 30 seconds and turn it back on does the problem appear again?
After a power cut we have to 'unlock' it and manually open it and when the power returns it stops closing about a centimeter before the lock engages so I have adjusted the striker plate accordingly but have now run out of adjustment so need the electronics adjusted. Haven't tried the DIY power cut as it could end up costing me again.
 
After a power cut we have to 'unlock' it and manually open it and when the power returns it stops closing about a centimeter before the lock engages so I have adjusted the striker plate accordingly but have now run out of adjustment so need the electronics adjusted. Haven't tried the DIY power cut as it could end up costing me again.
The reason for that is a safety factor.
Over the recent times where peaple have been injured or killed on electric gates closing on peaple.
 
The reason for that is a safety factor.
Over the recent times where peaple have been injured or killed on electric gates closing on peaple.

Yes I get the fact that it shouldn't automatically close when power comes back on. But it shouldn't need an engineer to come and visit.
 
How often and how long are the power cuts?

It may be worth investing in a small U.P.S to hold power to the gate controls

If this is the correct manual below, I can't see any settings that shouldn't normally be held in memory and no reference to loss of power.

The "decription gizmo" will only be a program presenting the settings in a slightly more user friendly view, and I supsect will hold a copy of your settings which can easilly be downloaded to your controller, saves scrolling through the menu with a button.


 
Last edited:
I remember our gate at caravan park was always troublesome.
This was for traffic and was the length of a road width… so sensed traffic going both ways.

Wasn’t for security… it just slowed traffic down enough so that we could read number plates off cctv.

It needed power to hold it down… so when there was a power cut, it opened under spring. Fail safe rather than fail secure.

We did get it serviced by the installers annually.. it is a specialised piece of machinery after all.

The problem ours had was on certain days, when the sun hit the optical sensors… the gate got confused and started waving up and down.. comical to watch… but no one could get in or out.. we had to manually switch it to always open.

Footage on YouTube somewhere… will have to find it..
 
Battery backup kits are available for the Thalia P system. However these are to allow the gates to function during power outages. Example below.

Hiwever, I still think yours is losing its settings due to a fault.

Screenshot_20220818-105742_Samsung Notes.jpg
 
How often and how long are the power cuts?

It may be worth investing in a small U.P.S to hold power to the gate controls

If this is the correct manual below, I can't see any settings that shouldn't normally be held in memory and no reference to loss of power.

The "decription gizmo" will only be a program presenting the settings in a slightly more user friendly view, and I supsect will hold a copy of your settings which can easilly be downloaded to your controller, saves scrolling through the menu with a button.


That's the manual. There is a heiroglyphic for closing distance but how you arrive at it and what it actually means are not shown. I attempted to ask BFT but they wouldn't talk to me because I was not one of their installers! They also informed the local installer who I'd used (only one for miles) that I'd been in contact with them!!!!!!!! Note that in order to get useful information from the BFT website you have to login and only installers have that privilege!
 

Reply to The 'Electric gate' scam in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Hey everyone, lately I've been trying almost everything to reduce the electrical noise over my Be Quiet Straight Power 11 850W 80+ Platinum PSU...
Replies
7
Views
2K
Hello all - I would really appreciate some advice please. I am conducting the groundworks to install a 6m opening "Hi Motion" sliding cantilever...
Replies
19
Views
3K
Replies
8
Views
8K
R
Good morning everyone, it has been a long time since I have asked for advice on here but I find myself at your mercy again. I have been asked by...
Replies
6
Views
3K
S
Having worked as an electrician for over 30 years and I've seen a lot of changes since the 14th Edition of the Regs. It seems to me that...
Replies
90
Views
10K
shagbite
S

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock