Discuss The mind boggles. in the UK Electrical Forum area at ElectriciansForums.net

U

urbanmonkey

Todays job was to investigate faulty outdoor socket and intermittent RCD fault, turn up, get to work, loop test on socket. No Earth, open it up to find the cpc wrapped in blue insulation tape and the box is full of water, so i'm thinking DIY, asked the customer who did it and they produce a cert, all filled in with clearly imagined readings by an NICEIC member! find the socket the outdoor socket had been spurred from( cable chased horizontally around a corner, chopped through a bit of wood supporting the stairs and then through wall into outdoor socket!), it's a spur, from a spur next to it, no Earth on any of them, whole debacle is supplied by downstairs RFC and the whole 3 of them installed by the 'competent person'

Proceed to have a quick look in the board to check RFC continuity and ramp test RCD with nothing attached etc. No continuity on L, N or E. fantastic. Proceed to start lifting laminate and boards, starting at the additions and towards where any sensible person may have got into the RFC, only to find two cables under floor with tiny bit of black tape around them, its the two legs of the RFC just cut and left live under the floor, right near the spurs upon spurs?! cable he had used to supply the spurious spurs from disappears in the direction of the front door under the floor, no sockets or expected cable routes to outlets in the vicinity.

Was gettin late so I Stuck a j803 on the unidentified cable and another on the two legs of the ring to restore continuity, tested it to make sure and going back tomorrow to tidy it all up and redo it properly, also have a look at no N continuity on upstairs RFC, he's been in there as well, fcu for an outside light, taken from socket in bedroom supplying a whacking great sodium discharge lamp with some kopex hanging from it, doubtless all taped up inside again!

No point reporting him I guess, he's paid his subs and thats all that matters to them. On the plus side I've picked up a fair bit of work lately from sorting out guff like this, I can't see it being long before somebody is seriously hurt or killed tho, find stuff like this almost weekly now.
 
Last edited by a moderator:
but if the customer reports it to niceic with a copy of your findings, something might just get done. q.v. uksparks thread from some weeks ago.
 
I spoke to them about the possibility of them reporting him to stop a potential death but they weren't really that keen on getting involved. Guy is apparently local but I've never heard of him. When he was called back as the RCD kept going his preferred test instrument was apparently.......wait for it.... a kettle.
 
The mind boggles!

An interesting post, and Fair Play to you for sorting it all out.

Can I suggest with lengthy posts that you use paragraphs to make it easier on the eye for readers.

Break down your pertinent points and break space them so that they are 'bite-sized' bits of information for people to read and digest.

Regards

Voltz
 

Reply to The mind boggles. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Helping out a friend and a CU change is really the best option as sockets in kitchen and downstairs room not on RCD protection. Now one of the WTF...
Replies
11
Views
1K
Old two core cable in a lighting circuit with no cpc at any point All points had metal fixtures and fittings class1 At two points the live loop...
Replies
0
Views
627
Hi, i live in a new build house where they builders have left a junction box on the outside of my house. In the junction box there is a 6mm twin...
Replies
14
Views
1K
Hi, I'm going to be installing an outdoor socket, have no problem with the outdoor/socket side, but when bringing the internal end or the SWA...
Replies
3
Views
707
I found a 13A FCU, connected to the kitchen ring supplying an outdoor junction box, providing two SWA 2.5mm radials. Unconventional? yes. One...
Replies
2
Views
819

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock