The Ghost

So I was called again to look at light in unit that has gone off. Of course when I got there it was on (again) The circuit is very straight forward, supply from Merlin Gerin DB 10a MCB supplying four twins. Checked all the connections for being tight including switch (wiggled and pulled) and securely fixed into termination points, all ok. Checked cable down to light from klix rose, ok. The fitting is HF with TriPhos tubes. The light stays on during this process no flicker.
So I have checked the cabling from the MCB to first light (which is the one with intermittent fault) and checked onward to the last light, four in all. No loose connections, all lights are working except this one, occasionally does not. As you may divine from the picture below it is not a situation (20 feet up) that lends itself to popping up with a tester and having investigations without a tower which is considerable expense. The cable (singles) is in plastic trunking changing to 20mm conduit as it progresses to each light. There is no sign of damage to the cables I can access, and have fought shy of putting up a tower due to cost and the landlord being a very very frugal person to put it charitably. Any ideas of a brilliant nature welcome.
IMG_3545.JPG
 
Do HF fittings suffer in the cold like ordinary fluo's?
I had an ordinary fluo in my garage that hated the cold and when I swapped it with an identical one used in the house then both worked fine - they both came from same supplier, on the same day, and fitted on the same day - so identical except one was a wuss!
 
Could be a dodgy lamp, does the fitting have one ballast for both lamps or one each? Most likely dodgy lamp or ballast.
I put a new HF flossy fitting (came with new lamp) in my dads garage a while ago, soon after he said the light would either not light or just flash then go off, put in a new lamp and had no bother since.
 
Replace the ballast. 6ft will have a PC2/70W and a 5 foot will have a PC2/58W. Some of the bigger wholesalers stock them too. Would be easier to do that off your ladder than the whole fitting! If it's non EM might be worth putting LED tubes instead. Less to go wrong.
 
A few questions please:

a. Does the fitting sometimes not illuminate when first energised and stay off? Or does it later illuminate?
b. Does the fitting sometimes illuminate immediately and later go off and stay off?
c. Is the fitting bathed in warm sunshine? The picture seems to show skylights in the corrugated roof.
d. At the first fitting at the end of the drop what is the L-N voltage before and after turning these lights on?
e. Any high amperage loads on the phase?
f. At any time is the fitting operating outside its designed temperature range? ie: first thing in the morning unit is cold.
g. Has the drop to the fitting been clamped excessively tightly deforming the live conductors? (I discovered this once on my wife's iron plug - an MK screwless clamp).
h. Is the Klix rose faulty? Change it if a check shows it is plugged in correctly.
i. Is there anyway someone could be playing mischief with the fitting or Klix rose.
j. Are the four fittings wired as a daisy chain or otherwise?
k. Is is a type B or C mcb?
l. what is the length of the run from mcb to first fitting and what is the guage of the live conductors?
m. Could you swap over complete fittings say 1 and 2 and see if the intermittent illumination moves with the fitting?
 
https://www.tlc-direct.co.uk/Technical/DataSheets/Lighting/HF.pdf

Have the correct tubes been installed in the fitting? I turned up this reference which has some advice on lamp compatibility.

I also learned that some fittings have switches in the end caps as a safety feature to isolate the contacts when no tube is present.

This reference-

Appendix B: Ambient Temperature and Atmospheric Conditions | Universal Lighting Technologies - https://unvlt.com/literature/troubleshooting/linear-fluorescent-lighting-systems-maintenance-guide/appendix-b-ambient-temperature-and-atmospheric-conditions.html

talks about the deleterious effect of low temperature on the ability of a ballast to start and run a fluorescent tube and also what happens when tubes do not reach their designed operating temperature.
 
Last edited:
I remember that the very early tubes had an earthed conductive strip along their length to aid starting. I suppose the same capacitive effect is achieved now by internal coatings and the proximity of the tube to its earthed fitting. So check too the connection of the cpc to the fitting, the continuity of the cpc back to the DB and that the reflector is electrically connected to the cpc.
 
Tad overkill for the one light?
Remember that this bloke is connected to the steel structure on a metal ladder and (within our firm) has to maintain three points of contact on said ladder. Throw a loop test into the mix and a RCD protected circuit then we're in for a show!
 
a. Does the fitting sometimes not illuminate when first energised and stay off? Or does it later illuminate?

No it works for 3 months the goes off for a few hours and comes back on totally at random. Then goes off after a few more months and goes back on in a few days etc.

b. Does the fitting sometimes illuminate immediately and later go off and stay off?

No See a.

c. Is the fitting bathed in warm sunshine? The picture seems to show skylights in the corrugated roof.

No it is not in any sunshine.

d. At the first fitting at the end of the drop what is the L-N voltage before and after turning these lights on?

Same, 246v

e. Any high amperage loads on the phase?

No there are no high A. equipment it is a kitchen with gas stove.

f. At any time is the fitting operating outside its designed temperature range? ie: first thing in the morning unit is cold.

No the unit has central heating which keeps the temperature ambient

g. Has the drop to the fitting been clamped excessively tightly deforming the live conductors? (I discovered this once on my wife's iron plug - an MK screwless clamp).

No there is no mechanical damage to any part of the lighting installation

h. Is the Klix rose faulty? Change it if a check shows it is plugged in correctly.

That is the only thing that has not been changed and thought to do that next.

i. Is there anyway someone could be playing mischief with the fitting or Klix rose.

Not a chance

j. Are the four fittings wired as a daisy chain or otherwise?

Daisy chained one after the other

k. Is is a type B or C mcb?

Type B

l. what is the length of the run from mcb to first fitting and what is the guage of the live conductors?

1.5mm² 7 m.

m. Could you swap over complete fittings say 1 and 2 and see if the intermittent illumination moves with the fitting?

A lot more trouble than it is worth, might as well rewire it if I am going that far
 
Unlike a choke, which is simple and usually either works or doesn't, an HF ballast is an electronic switched mode power supply, containing many dozens of components (some of which have finite lifespan) and connections. Intermittent faults are not only possible but likely. If the lamp is new and good and the endcaps undamaged, I would have changed it by now.
 

Reply to The mystery of the intermittent fault on flourescent light in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
661
Hi all, Wondering if you could offer some advice please. I carried out a small outdoor lighting project today at a commercial property. 4 lights...
Replies
5
Views
931
Hi all, Was speaking to a family member recently, he told me his iron recently made a bang and flash as he plugged it in to the socket, and could...
Replies
14
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock