Search the forum,

Discuss This seems very dangerous... in the UK Electrical Forum area at ElectriciansForums.net

Dave_

-
Reaction score
24
Went to a house today fault finding, RCD tripping....

Faulty RCD but thats not the issue.

I noticed that there didnt actually appear to be a main earth.

The supply upstream of the meter and teleswitch (now out of use) is a pyro that is a single core 10mm with a strap on the sheath that provides the NEUTRAL (no earth in sight!)

The mains position including the meter, DB & teleswitch was moved around 5 years ago by what the client claims is a competent spark who had all the papers and did provide paperwork at the end of the job. I asked for the paperwork but client said could be difficult to find it. Meter seals and teleswitch seals cut in all the places needed to move the equipment.

Im guessing that the flat was originally supplied with 2 single core 10mm pyro's and some numpty has snapped one when moving the mains to its new position then not done the proper thing of reglanding the pyro, or whatever he needed to do safely get it back in service.

If that is the case that pyro is buried under the floor in a wall somewhere now. I tried to access the mains intake cupboard. Not FB keylock, need to now contact the council. I need to see that cupboard as if there were two 2 SC pyros then ill find he has had to connect the sheath of the one in service to the neutral bar. There is probably a Ryefield cupboard there.

All in all though the client is gonna get a huge bill as its the DNO that is going to have to put it right as its all upstream of the meter so im not touching it.

I took a few readings. Im guessing its a TNS system as its a 60's block with pyro supply. ) 0.29 ZS. Cant do a ZE as there is no earth! Your probably wondering what is providing the earth? Its the cooker CPC, connected to a gas hob connected to the gas supply. there is bonding in place. But basically they are relying on the gas pipes as a main earth.

I told the client its very dangerous and if I rang NICEIC technical they would most likely advise to isolate the installation. Its been like this for 5 years (no excuse i know!) I didnt switch it off but said ill be back tomorrow with Hackney council to get in the cupboard and find out exactly what is going on.

Any thoughts on this??
 
Ive seen this before, and I questioned it.

Various council estates in North London have this method, still in service. 10mm single core with the sheath (PVC insulated) as the earth/neutral conductor.

Edit: Hackney council probably own this cable, so it should be them responsible for maintaining it, but I doubt they will do anything with it to be honest.
 
I did wonder if it was acting as a PEN conductor but the strap goes from the pyro sheath through the meter then straight into the main switch. nothing goes to the earth terminal whatsoever.
 
I did wonder if it was acting as a PEN conductor but the strap goes from the pyro sheath through the meter then straight into the main switch. nothing goes to the earth terminal whatsoever.

The ones I have seen have the pyro glanded into an adaptable box, where the link is made between N and E, then Live Neutral and Earth go off into the CU.

(Good luck with the council :86: !!)
 
Apologies for the late reply! I forgot...

I visited site the other evening to discover it was a PME system. At the service head there was three pyros that were single core 10mm each with 2 pyro straps around the sheath one to neutral bar one to earth, then obviously connected together.

Easy job - just a case of connecting supply neutral to MET at the CU. retested Ze and got 0.19 not 1.19 or thereabouts!

Makes sense I suppose. That pyro lateral main being a concentric cable, and I suppose the sheath can take a whopping amount of current.
 
If this cable is upstream of the meter then its on the clients side then there is no way you should combine earth & N only the supplier can do that or have i misread the OP ?
 
Ok so if you have a installation that is not earthed and you have to deal with a council that just tries to fob you off, you speak to 10 muppets in an office before getting anywhere and they usually take weeks to come out....

Or...

You have a henley block for the neutral connection next to the board. A simple connection between the two and the installation is safe and I get paid.

Or get the council out and their guy connects into the henley block and I connect it into the MET.... Hmmmm
 

Reply to This seems very dangerous... in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all. Sort of an interesting one. I had a call from a client to say she is getting a shock when using the shower. I told her not to use it and...
Replies
15
Views
2K
Hi all I am after some advice on an installation I have coming up. Its a new TP+N circuit in SWA (13m run clipped direct) for a 22kW Tesla wall...
Replies
1
Views
195
Morning all, Really hoping to get some advice / confirm what a few of us are thinking about a job in the future. Back ground - We have to swap...
Replies
15
Views
489
Hi all, So my factory needs more power, currently 100A/3p (70KVA) => 400A/3p (200KVA) UKPN wont upgrade existing supply and are insisting on new...
Replies
1
Views
415
Hi all, any recommendations for neat and complaint ways to "house" a new supply -- the main electrical fuse, cut out, meter etc that on our house...
Replies
7
Views
867

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top