I have two FCU's in the same room. Can these two FCU's (3 phase) be fed from same cable from the panel located in the another room? Is it acceptable as per codes? or do I need to run separate cables?
 
I believe Saudi Arabia uses BS7671.
As long as the Current Carrying Capacity of the cable is equal or greater than the load from the 2 FCUs, what you propose is fine.
The link between the 2 FCUs can even be sized according to the load on the 2nd FCU (if you want).
 
I have two FCU's in the same room. Can these two FCU's (3 phase) be fed from same cable from the panel located in the another room? Is it acceptable as per codes? or do I need to run separate cables?
What exactly do you mean FCU 3phase?
 
I mean the three core (Multicore) Power cable running from the panel to the FCU 1 and then from Junction box / Switch Isolator, another cable will be connected to FCU2
In the UK when people speak of an FCU it usually means a single phase switch plate usually used to connect single phase appliances, this is where the confusion has arisen.
 

Reply to Three phase - serial connection in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a scenario where there is a three phase DB in a commercial property where there are mixture of three phase and single phase washing...
Replies
2
Views
844
Hi, searched the forum but cant locate anything similar so apologies if ive missed something. Ive got a new hob to install in the kitchen...
Replies
5
Views
1K
Hello, We are converting a former office into 10 self-contained flats with kitchens, showers, heaters all electric, no gas. We have been offered a...
Replies
1
Views
721
Good day to you. I need electrical drawings urgently and hopefully there is someone that can assist me. They are all for electrical trade test...
Replies
6
Views
803
  • Question
Hi All. I need to extend the cables for a 3 plate ceiling rose/pendant on ground floor ceiling by 450mm. Can I fix the ceiling rose/pendant to...
Replies
5
Views
376

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock