Discuss Three phase upgrade question in the UK Electrical Forum area at ElectriciansForums.net

canron

-
Reaction score
1
Hello all...hope someone here can help....


currently have three phases coming in to the property (old farm) but only receive single phase with a single phase meter. The overhead cables were upgraded a few years ago so the cabling up to the meter is all fairly recent, I can see the 3x100amp fuses on the grids side of the meter, only one is used

the supplier is asking for 'maximun load reading for each phase' and 'maximum load in kVA expected for the site' which they say they need so they can determine what kind of upgrade is required.

I could total up all the lights/appliances for the site maximum but what do they want to know when asking 'maximum load reading for each phase'?

I thought it would just be a case of changing the meter...
 
What are you adding to need to have to upgrade to 3 phase?

As above the supplier has to establish whether the supply up to your house is able to cope with the new demand.

If you're adding a lot of extra load you could end up paying not only for a new local transformer but cabling back to the next one and a larger transformer there as well etc, etc.
The cost could be anything from a few pounds to tens of thousands of pounds.

You need to supply them with accurate figures with professional assistance.
 
it's a woodworking machine with 2 motors - (looking at the plates) one is 4kVA, other is 1hp, so not much at all
maybe smaller sized machines in the future but only ever one operating at any time

surely the 3x100A that comes in just now is sufficient?

or am I missing something?
 
Well he is (missing something), a three phase meter and supply. Think you may have to be careful so you don't get penalty charges they are bringing in next April though and be accurate with your maximum demand figure in Kva.
 
Looks like I'll have to get someone else in to be safe....

I asked an electrician, he said the only thing that matters is the max demand figure. Told him what it was for...he just said to put 60-70 kVA.

As I say I don't even know what they're looking for in the 'maximum load reading for each phase'...is this also an estimate or an actual reading with a clamp meter or similar?
 
Well he is (missing something), a three phase meter and supply. Think you may have to be careful so you don't get penalty charges they are bringing in next April though and be accurate with your maximum demand figure in Kva.
What penalty charges are they could you explain more please Vort.
 
A 3 phase supply needs to have a balanced load across the phases, if you do get a 3 phase supply your existing single phase DB would have to be changed to 3phase and the circuits split equally (or as best they can) across the phases. I've also heard that unbalanced loads are charged (electric bill) on the phase with the highest KWh for them all.
EG L1 - 4532 KWh L2 - 3674 L3 - 2236 you would pay the highest 4532 for all 3 phases
 
Last edited:
A 3phase generator might be an option, may be cheaper if the supplier decides to charge a fortune to install supply
 
I initially intended to go for a converter....before I saw the plates on the motors (I told them it was a 7.5 and 1kw motor) I was told I'd need a rotary converter as one of the motors is for a hydraulic pump which needs a lot of torque.....The model they recommended was about £1500...

So thought getting actual 3 phase (since the wiring is already there) might be a better option. Starting to doubt that now!
 
Someone I knew wanted 3 phase on his farm, although he had single phase, the overhead cables were literally passing on the road near by....supplier wanted 10grand to install 3 phase and that was several, maybe more years ago!
He has a diesel generator and runs it on cherry!
 
For one machine a genny might be a bit much...the machine would only operate for 5-10 mins at a time, sometimes could go a few weeks without using it but it's essential. Any 3phase gen I've seen are a fair few thousand...will have a look tho!

The supplier said about £300-400 to change the meter....if its going to be multiple thousands I'll definitely be leaving it!

As I say initially I thought the hydraulic pump motor was 7.5kw but turns out it's 4....so maybe don't need as big a converter as first thought
 
What penalty charges
Excess capacity penalties for half hourly electricity supplies - https://www.theenergydesk.co.uk/excess-capacity-penalties-half-hourly-electricity-supplies/ I did not know about these until @Leesparkykent mentioned penalty charges in a post I made recently. So a bit of research found the above. I think the giveaway is when they ask for the supply needs in Kva. However if you do get penalty charges you just re-negotiate your maximum supply demand.
 
How many different grades/capacities? Are there for 3x100amp coming in to the property?

I've seen 45kVA (seems low) and 70 kVA mentioned...are there others?

Also balancing the load...will they bill 3x the highest used phase?
 
Last edited:
As a dno employee, it sounds as if you just need a straight forward meter change. You're load is well within the 100 amp supply. Just put the estimated load per phase. Don't worry about changing the existing customers, only needed if you have a high load on one phase creating problems. So 50 amps P1, 20 p2 , 10 p3 is not a problem. Half hour metering only applies to large power, where the MD ( maximum demand) is measured every half hour, if it goes over the agreed MD you pay extra.
 
Looks like I'll have to get someone else in to be safe....

I asked an electrician, he said the only thing that matters is the max demand figure. Told him what it was for...he just said to put 60-70 kVA.

As I say I don't even know what they're looking for in the 'maximum load reading for each phase'...is this also an estimate or an actual reading with a clamp meter or similar?
It’s basically a load sheet from the power company
 

Reply to Three phase upgrade question in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a scenario where there is a three phase DB in a commercial property where there are mixture of three phase and single phase washing...
Replies
2
Views
851
Hello, I'm new to this forum, we are in the process of converting into 12 flats all electric, no gas incl. heating, showers etc. An electrician...
Replies
10
Views
2K
I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
1K
Hello, We are converting a former office into 10 self-contained flats with kitchens, showers, heaters all electric, no gas. We have been offered a...
Replies
1
Views
723
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
653

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock