I want to understand the concept for through faults in case of transformers.
For example, there is an external fault on secondary side of a generator step up transformer, so when it is said that all through current will pass through the transformer, does it mean that current is now flowing in opposite direction i.e. from the system in to the transformer & generator? If yes then what could be its effect on transformer or generator? Please explain
 
Depends on the context you mean. From your question it sounds as if you are thinking of a Generator, feeding to a distribution network through the step up transformer with a fault occurring on the transformer secondary..

Any fault on the secondary side of the transformer will provide a fault current from the generator and also a fault path from the distribution network. The generator current will be limited by the impedance of the transformer. Any fault on the HV side with a distribution network connected is likely to catastrophicaly destructive to equipment before the HV networks protection kicks in.

There should be no flow of fault current from the system to the generator, since it would take the easiest path available to it, which in this case would be the fault on the transformer secondary.

A simple single line diagram to better explain your question would help.
 
Last edited:

Reply to Through Fault Current in the Canada area at ElectriciansForums.net

Similar Threads

Hi everyone, I wondered if anyone could help me with something that has been niggling me please?! When a Solar PV feed in circuit is installed...
Replies
14
Views
1K
Hi, plumber here so please be gentle (or take the p-ss ;) ), I am supposed to be installing a UV water steriliser for a customer. I have some...
Replies
16
Views
2K
If we had 4 appliances to power, one in every room of a house, Once the current passes through them all, the remaining voltage & current is said...
Replies
12
Views
2K
Hi all, Im new to the forum and wanted to check something and maybe get some advice confirmation. Ive got halogen wall lights which use a...
Replies
6
Views
1K
I currently have a 3Kwh solar PV system which was installed over 12 years ago and getting a very good FIT payment and I don't want to lose it! I'm...
Replies
0
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock