Thanks Engineer 54 , i had never heard of the x3 recommendation .

That's because for RCDs it doesn't happen. As Eng 54 has said.
I rather think the x3 refers to discrimination of fuses, mcbs etc.

Lets say you have a 300mA RCD main switch(non time delayed) and sockets protected by a 30mA RCD.
Which RCD will trip first if there's a big earth fault on one of the sockets of more than 300mA? Its the RCD with the faster (time) trip characteristic or it may depend on where the AC sine wave is at. It could really be either, or - sometimes - both of them.

An S-type is the only way to ensure discrimination of RCDs.
 
Thanks Taylortwocites , that would generally be the case as you say . It was the 3x rule of thumb that i have not heard of before , well for RCD's anyway . :smile:
 
That's because for RCDs it doesn't happen. As Eng 54 has said.
I rather think the x3 refers to discrimination of fuses, mcbs etc.

Lets say you have a 300mA RCD main switch(non time delayed) and sockets protected by a 30mA RCD.
Which RCD will trip first if there's a big earth fault on one of the sockets of more than 300mA? Its the RCD with the faster (time) trip characteristic or it may depend on where the AC sine wave is at. It could really be either, or - sometimes - both of them.

An S-type is the only way to ensure discrimination of RCDs.

No, this was a stated quite clearly in a few of the manufactures catalogs in the past, Merlin Gerin, Siemens being two of them.

Discrimination using this method (without a time delay) say a 100mA upstream of a 30mA, only works with increasing natural leakages, any fault on that downstream circuit that produces a fault leakage current exceeding 100mA, ....and both RCD's are likely to trip simultaneously.

As you say, all RCD's/RCBO's have a pretty wide ranging tripping speed, which can also affect discrimination between series connected RCD devices. But the only way to ''Ensure'' discrimination in all normal circumstances, is by means of an S type device being used upstream...
 
i thought you needed the 100ma as main switch if the cu was metal.that seems the norm on the ones ive seen

I may be wrong , but if using a metal cu it will need a insulated shield around the incoming part / section of the cu to give extra protection to the tails before the rcd .
This may not be applicable now days , but it seemed to be standard practise on nearly all of the older TT boards i have come across ?
I hope you do not mind me asking Engineer54 ,or anyone else to that matter .
Was this the case in the past or have i been misguided to believe so ?
 
I may be wrong , but if using a metal cu it will need a insulated shield around the incoming part / section of the cu to give extra protection to the tails before the rcd .
This may not be applicable now days , but it seemed to be standard practise on nearly all of the older TT boards i have come across ?
I hope you do not mind me asking Engineer54 ,or anyone else to that matter .
Was this the case in the past or have i been misguided to believe so ?

i think the 100ma is to protect the tails on metal clad boards,tho it may be omitted now if using insulated seals as you say but dont quote me on that

unlike the pic shown in the onsite guide,the 100ma was normally a stand alone unit placed between the meter and the cu if metal clad,the main switch was a standard main switch in the cu.
 
Last edited by a moderator:
Sorry Alarm man , got the wrong end of the stick with your post .
I took it that you meant the main switch was in the cu and not a stand alone !:49:
 
Sorry Alarm man , got the wrong end of the stick with your post .
I took it that you meant the main switch was in the cu and not a stand alone !:49:

sorry thats why i edited mate,did sound confusing..

to edit again,the osg pic of tt is confusing too,just states additional protection required in using metal clad cu,so as you said insulated glanding into board,(ive read it somewhere) or swap the 100ma in the cu with a main switch and fit a s/a 100ma between the meter and cu
 

Reply to time delay rcds in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

See this time after time - poor installation: new split load board on a re-wire tt installation. The main switch is not a time delay rcd. The...
Replies
2
Views
348
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
958
Hi I'm looking for some advice for adding a time delay on my parent's shower room fan. My parents had a section of their garage converted into a...
Replies
8
Views
1K
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Im suppling distribution circuits and want to use the largest possible RCD available to avoid nuisiance tripping (its for outdoor street furniture...
Replies
2
Views
896

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock