I have just carried out an EICR at an old property and found this issue with the main earthing conductor.
It has a TN-S system but the earthing conductor emerging from within the taped up tar coating just before the cut out is only 4mm2 of (what looks like) steel wire armourings. It is 100mm long connected to a small earthing bar. It is not the more popular lead sheathed with earth clamp moulded to it.
My question is, as there is no way to upgrade it without getting involved with DNO cable/equipment, should I just leave the 4mm earth and earthing block close to cut out, then upgrade all earthing from that point on.
Just to point out, at present there is only 4mm earth feeding a BS3036 consumer unit (due for replacement) with 6mm earthing to gas and water. The Ze reading is 0.17 ohms. Adiabatic calculates earth should be 6.19mm2.
Also, what codes for the DNO's undersized earth?
 

Attachments

  • IMG_20210109_093124.jpg
    573.5 KB · Views: 69
It will not be 4mm it will be an imperial size which I think is just bigger than 6mm, anyway it is not part of the instalation it is part of the DNO supply
 
OK big thanks guys. Makes sense to be imperial size due to age. It just looked smaller than standard new 6mm earth but sometimes hard to tell.
So my best bet is to leave alone. Leave earth block in place and just upgrade gas + water bonds and new earth to a new DB from the existing earth block.
Also I forgot to mention in last post (maybe I should start another thread) that the tails from cut out to meter and meter to DB are definitely only 10mm2 fed by 60A BS88 fuse in cut out (there are no seals on the cut out so I could remove easily). This seems very borderline to me. I am surprised a smart meter was fitted 3 years ago with such small tails left in place!
 
OK big thanks guys. Makes sense to be imperial size due to age. It just looked smaller than standard new 6mm earth but sometimes hard to tell.
So my best bet is to leave alone. Leave earth block in place and just upgrade gas + water bonds and new earth to a new DB from the existing earth block.
Also I forgot to mention in last post (maybe I should start another thread) that the tails from cut out to meter and meter to DB are definitely only 10mm2 fed by 60A BS88 fuse in cut out (there are no seals on the cut out so I could remove easily). This seems very borderline to me. I am surprised a smart meter was fitted 3 years ago with such small tails left in place!
Why change the main bonding?
 
The landlord has asked me to put right whatever it needs for a satisfactory cert so new DB goes without saying. New earthing from main earth block to DB as its currently less than 6mm. As I've gone this far, it makes sense to upgrade gas and water bonds as they are within same cupboard/area and easily enough to do although I could get away with leaving them as 6mm. Its just for my peace of mind that its done just out of good practice, and the landlord is happy to pay so why wouldn't I upgrade?
 
The landlord has asked me to put right whatever it needs for a satisfactory cert so new DB goes without saying. New earthing from main earth block to DB as its currently less than 6mm. As I've gone this far, it makes sense to upgrade gas and water bonds as they are within same cupboard/area and easily enough to do although I could get away with leaving them as 6mm. Its just for my peace of mind that its done just out of good practice, and the landlord is happy to pay so why wouldn't I upgrade?
I agree with you here I have two rules which I like to stick to. CSA of main earth should be at least half of supply conductors. Also within a TN earthing system should be minimum of 10mm. I do think a 6mm is undersized and needs upgrading just ring the DNO and speak to them I’ve done it many times and sub contracted work from them in my area after speaking to them
 
Seen loads of these I always make a note on Eicr,Upgrade of Rec MEC required never know if it’s actually done.
doubt if they ever do. that short bare bit of cable will handle fault current for the duration of the fault without melting or setting the house on fire.
 
doubt if they ever do. that short bare bit of cable will handle fault current for the duration of the fault without melting or setting the house on fire.
Agree,can you imagine us doing that,NICEIC would have a heart attack.
He nearly had one when I asked about bonding.
 
I do think a 6mm is undersized and needs upgrading just ring the DNO

Why? (in the general case, acknowledging that there are situations where it is clearly true)

Do you have evidence of bare 7/.044 conductors failing to clear a 100A BS1361? Or does a larger conductor just 'feel' more suitable?
 
the solder to the lead sheath would melt before that bare bit of 7/.044 overheated.
 

Reply to TN-S earthing issue in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I've tried to understand one way or another but this seems to be connected to the DNO fuse/cutout, and then loops down (out of sight) and comes...
Replies
2
Views
754
Trying to understand why car chargers attract this earthing ballache. from what I learnt it's all about the rare times a Neutral / PEN conductor...
Replies
6
Views
2K
Morning guys, Just been to look at a CU change and there was a bit of an oddity with the PME connection in the old black cut out. Looking at the...
Replies
2
Views
612
Hi all, After months of waiting, the fused neutral cut-out at my parents house has been replaced but I am concerned about the main earth. I...
Replies
6
Views
3K
I am installing a Victron Quattro in an island mode configuration (in the UK, the DNO is the NG). I will be adding a stand-by generator. My...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock