So I went to see a job yesterday, its a house converted to 3 flat. Fairly good install, dual rcd board feed directly from tncs cut out. I ask where the meter is and she pointed me to the cabinet in common area downstairs where main incomer is located along with 3 meters for each flat. As you can see in pics there is no earth provided there and they separated pen at consumer side of the installation. My understanding is that it should be separated before the meter. I am going to call dno to check what records of this install they have.
Property is in London so earth should be provided by dno.
Black meter belongs to the client
Any thoughts on this one?