Did a lot of miles today and was pondering.

This is not a real scenario.

Not necessarily "how often does a Ze make an installation impossible?" but more..

If, the measured Ze is say 0.30 Ohms and you then design your installation to keep your Zs's within BBB max allowances, does the DNO have a responsibility to maintain the measured Ze or can they simply state 0.8 Ohms.

For an example you install a 10KW shower.

At time of installation the Ze is 0.3 Ohms.

Your R1+R2 is 0.1 Ohms, Zs of Approx 0.4 Ohms.

10mm T&E on a B50 Zs limit = 0.69 Ohms.

So, job done, cert issued and notified.

Stay with me....

6 months later there's a change of tenancy and the landlord has an EICR done. I nkow

Now the Ze is 0.6 Ohms and my installed circuit is measured as 0.7 Ohms and is listed as a C2 on the cert.

What happens, will the DNO just state "0.8 Ohms not our problem"
 
If the Ze is within stated values as supplied by the DNO I tend to think they will not take any action. Sometimes it is possible to talk with someone and discuss that change and there would be a slim possibility they may check their earth. They are required to maintain the earth as required under ESQCR (24) but whether they would see a legal responsibility to do so in the scenario described I think is remote. And the figures you have shown suggest a change from requirements of .01 ohms so would that be a C2? But anyway the 80% rule applying would mean a significant non compliance I agree. Difficult as to how they would propose to remedy such a C2
 
why are we as sparks so pedantic about things,in my opinion a discrepancy of anything like 0.05 ohms is irrelevant due to all sorts of things ,different meters ,tightness of croc clips, unclean conductor connections etc etc .the dno in my experience would take no action.
 
Might be wrong, but aren’t those values given ‘typical’ values not maximum, and the DNO may or may not try and reduce them, if it exceeds the typical value.
 
I've seen 1667 Ohms listed as max Zs on EICRs before where RCDs are present but thought it was frowned upon, relying on an RCD for fault protection.
An RCD is a permitted device for earth fault protection on a TN system, I dont have the BBB to hand for the reg number but it is (obviously) in the section on fault protection for TN systems! and clearly states the maximum Zs in the table for RCD's applies (41.5 off the top of my head ??). A lot of electricians simply dont accept it, but technically, where a 30ma RCD protects a circuit the maximum permitted Zs is 1667 ohms regardless of the earthing system.
 
An RCD is a permitted device for earth fault protection on a TN system, I dont have the BBB to hand for the reg number but it is (obviously) in the section on fault protection for TN systems! and clearly states the maximum Zs in the table for RCD's applies (41.5 off the top of my head ??). A lot of electricians simply dont accept it, but technically, where a 30ma RCD protects a circuit the maximum permitted Zs is 1667 ohms regardless of the earthing system.
411.4.5, 411.4.204, and table 41.5
 

Reply to TNS Ze 0.8Ohms in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello there. I've been looking around here and found some conflicting information. I have a question if I may ask. I had an electrician come over...
Replies
30
Views
4K
Hi, first question on here in a very long time, I am hoping for some nice replies ?. It's been playing on my mind all week and can't seem to find...
Replies
12
Views
4K
Hi, installed some circuits in a factory. The circuits were tapped off of a busbar that goes straight to the main switchgear. From this I...
Replies
3
Views
2K
I'm doing an EICR on a static caravan after being called on to fix to a couple of problems due to loose connections. It's all fine now within...
Replies
4
Views
6K
I understand how to test Ze and Zs and that Zs is the total impedance from the suppliers tranny to the final accessory in a circuit your testing...
Replies
51
Views
12K
Deleted member 26818
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock