Back in the 80s I was an installation inspector for the local electricity board and before fitting a meter we had to check that the earth loop impedance was below 0.8/0,35 ohms.
You should always design to the maximum stated value as the DNO may reconfigure their network without notifying the customers.
A typical example is the PSCC the 16kA is based on you being right next to a substation with a 3 meter long service cable. You may know that the substation is a 300 meters away the DNO will say that they may but a new substation right next the house in 10 years time.
Some DNOs allow you to reduce the 16kA if you know the distance between the point of supply and the nearest footpath, again even if you know the main cable is across the road, it may be moved in the future. Appendix 14 says you do not need to measure PSCC in a domestic installation if the DNO declare it at 16kA.
My understanding is that you can use 6kA mcbs as long as they are in a type tested enclosure backed up by the DNO fuse, cant remember where that is written down though.
 
Back in the 80s I was an installation inspector for the local electricity board and before fitting a meter we had to check that the earth loop impedance was below 0.8/0,35 ohms.
You should always design to the maximum stated value as the DNO may reconfigure their network without notifying the customers.
A typical example is the PSCC the 16kA is based on you being right next to a substation with a 3 meter long service cable. You may know that the substation is a 300 meters away the DNO will say that they may but a new substation right next the house in 10 years time.
Some DNOs allow you to reduce the 16kA if you know the distance between the point of supply and the nearest footpath, again even if you know the main cable is across the road, it may be moved in the future. Appendix 14 says you do not need to measure PSCC in a domestic installation if the DNO declare it at 16kA.
My understanding is that you can use 6kA mcbs as long as they are in a type tested enclosure backed up by the DNO fuse, cant remember where that is written down though.

434.5.1


Plus some words it would appear
 
let through bs88.png


Even a typical let through for BS88 fuse

You doing the 18th or 18th amendment 1? :)
 
Doing SELECT 209 initial verification and 214 periodic inspect and test. Not too bothered about amendment 1 as I have never got involved with vehicles, yet.
 
Agree, but if the limit as defined in the 18th is used, then just like everything else, I have a valid defence in court should something happen.
But BS7671 does not define any limit. In fact it is wholly outside the scope of BS7671.
[automerge]1581423808[/automerge]
Interesting topic. If we were to design according to our DNO's quoted values, rather than measured, this would presumably include the max quoted fault current. In Western Power's case this is 16kA (single phase, LV), which would mean I would be unable to fit standard 6kA breakers in all circumstances.
The conditional rating arising out of Annex Zb (previously Annex Za) means that is not the case.
 
Agree, but if the limit as defined in the 18th is used, then just like everything else, I have a valid defence in court should something happen.

Where is it defined in BS7671?
[automerge]1581426681[/automerge]
Interesting topic. If we were to design according to our DNO's quoted values, rather than measured, this would presumably include the max quoted fault current. In Western Power's case this is 16kA (single phase, LV), which would mean I would be unable to fit standard 6kA breakers in all circumstances.

Incorrect, the cutout fuse provides backup protection for the potential 16kA as long as those 6kA devices are in a suitable type-tested assembly
 
But BS7671 does not define any limit. In fact it is wholly outside the scope of BS7671.
……..

Oops, forgot it's actually only in the on-site guide (and perhaps GN3), I know the quoted figures were actually defined in ER P23/1 - with caveats for rural sites of course, and that these are no longer the values since the introduction of P23/2 recently, but my point is that if I adhere to proper guidelines I am better covered than hoping for a low value on the day.
 

Reply to TNS Ze 0.8Ohms in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello there. I've been looking around here and found some conflicting information. I have a question if I may ask. I had an electrician come over...
Replies
30
Views
4K
Hi, first question on here in a very long time, I am hoping for some nice replies ?. It's been playing on my mind all week and can't seem to find...
Replies
12
Views
4K
Hi, installed some circuits in a factory. The circuits were tapped off of a busbar that goes straight to the main switchgear. From this I...
Replies
3
Views
2K
I'm doing an EICR on a static caravan after being called on to fix to a couple of problems due to loose connections. It's all fine now within...
Replies
4
Views
6K
I understand how to test Ze and Zs and that Zs is the total impedance from the suppliers tranny to the final accessory in a circuit your testing...
Replies
51
Views
12K
Deleted member 26818
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock