Hi Darkwood

Reg 411.3.3 I think (a) is so open, I believe the wording will be changed in the amendment 1 (b) you could stick a label on each socket outlet?

Regards
They are 25ft up hidden in a pearling so out off reach and only a maintenance (trained) person or sparky would spend all the money on a scissor lift to change any faulty fittings so not going to code it, and all he will do is unplug the fitting making the task safe.
 
They are 25ft up hidden in a pearling so out off reach and only a maintenance (trained) person or sparky would spend all the money on a scissor lift to change any faulty fittings so not going to code it, and all he will do is unplug the fitting making the task safe.


Hi Darkwood


He might plug in a lawn mower while he's up there. I know what your saying that's why I would go back to the risks of to fit or not to fit a RCD.

Regards
 
Hi all.

I've used the plug and socket outlet method before on a few installs, but we used MK "T" earth socket outlets and plugs thereby making them non-standard sockets and eliminating the need for RCD.

I've used kliks many a time too, only issue I have is terminating the bleeders into a galv conduit box.....particularly when wired in 4mm 3c swa due to loading and VD.
 
No RCD required a stated due to the nature of the install.

One other thing to consider: If the fluorescents are high frequency they will leak current to earth or they will not work. Try putting large quantities of these babies on an RCD and watch it trip !
 
Are they standard socket outlets? the reason I ask is that if they are non standard ie pins turned 90 degrees etc only the lighting could be plugged in.
 
Are they standard socket outlets? the reason I ask is that if they are non standard ie pins turned 90 degrees etc only the lighting could be plugged in.
Standard sockets but its not a problem they are 25ft up in the perlings i like to see the cleaner try use them :D
 
Protection by 30mA RCD not required for socket outlets under the control of skilled or instructed persons.

Does this mean that I don't need an RCD in my house

I can say that I'm com.... compe.... compet..... competent person (got there in the end) and my other half, her son, and my mother in law are all people under instruction?


Can I be a cheapscape and just use main switch and MCB?


(I am taking the pee here and just debating)

:)
 
Last edited:

Reply to To be RCD or not to be RCD in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

hi all come across a new build commercial office where radial circuits feeding electrak power track was protected by 32A RCBO at dist board and...
Replies
15
Views
1K
Evening all, If a socket circuit is not RCD protected via an RCD/RCBO and there isn't the option of fitting an additional RCD enclosure or...
Replies
20
Views
6K
Did a couple of inspections on 2 x 2 bed ground floor flood damaged flats today, only 4 circuits in each, bizarrely one socket circuit and 2...
Replies
6
Views
2K
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K
Hi guys I have some industrial lighting circuits to wire in a workshop and was after some fresh ideas/suggestions as to how i could best do this...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top