Hey there, I don't normally post much on here but am always browsing through this forum as the topics are somewhat interesting.

Anyway, as per the title. I managed to end todays work with a BOOM!

I have been working on a complete refurbishment on a old 1920's terraced house. The property has a dedicated resin supply cable feeding a single phase meter which then feeds a consumer unit. After stripping out all the cables throughout the property only leaving a temporary socket, you would assume every cable in the house is dead, right? WRONG!!

Today I had to ease of a sheet of wood that the electrical cutout/meter was fixed to so that the plasterer could dry line/plaster the wall behind it. That was easy. He then came back to me and asked if this other cable sticking out of the wall also dead?, I went back to the cupboard to discover an old 6mm lead cable poking through the wall with the end taped up. I told the plasterer "Of course its dead, the only cables in this building that are live are the temporary sockets". As i finished the sentence I was already halfway though cutting the cable. Then BOOM!!!!!! The sound of a £30 pair side cutters turning to ash along with some fireworks for added effect.

After scratching my head and wondering how the hell the old cable could still be live I then ventured into next doors property...

After opening her electrical cupboard and letting out the smoke I had created, I spotted the old LEAD cable going into the suppliers side of her old cast iron fused live/neutral cut out. The funny thing is was that her house was still on so the smoke in the cupboard must of been the old lead cable turning to ash!!

I told the lady that she needs to call the electrical provider and for them to send out an engineer ASAP.

Ive never seen this is 16 years of my electrical profession, but apparently this is how properties were supplied pre 1950's.

The funny thing is that the neighbours electrical intake had a new meter and consumer yet noone had pointed this out to her!!

What a great way to end a weeks work :)

Mike
 
Last edited:
Haha, never and i mean NEVER assume things are dead.

When i was doing my apprenticeship i asked if the power was off so i could change a socket faceplate - "yes mate" was what i got told and my first electric shock followed approx 20seconds later.

Then my boss said, "never assume, i knew it was live you should of tested it" ... old school approach to electrics but it has definitely taught me a lesson that has stuck with me for life.
 
I rewired a property and had the board shut off, we were chopping all cables off from sockets and switches. Most socket outlets where fed from the cavity, I went to cut of a socket and my cutters went bang and the next door neighbour came knocking, "my powers gone out, anything to do with you". You can imagine what happened next, a bit like neighbour wars. I went round next door and removed the spur from one of her sockets.
 
Nice to see safe isolation was carried out. Hope you have made your insurance company aware that you very nearly killed someone at work. Hopefully you told your employer too so they can suitably deal with a liabilty like yourself.
 
Nice to see safe isolation was carried out. Hope you have made your insurance company aware that you very nearly killed someone at work. Hopefully you told your employer too so they can suitably deal with a liabilty like yourself.

Haha welcome back to this forum Dilb :waving:
 
It came off the live side of the cutout DILB... I believe the OP made the assumption to his cost that this cable was unused and not the property of the DNO, the DNO may now issue a bill for the repair as it wasn't due to failure on their part.
 
As I mentioned, safe isolation just because you think its dead doesnt mean it is. Surely any competant electrician knows this?
 
Last edited by a moderator:
As I mentioned, safe isolation just because you think its dead doesnt mean it is. Surely any competant electrician knows this?
I wasn't picking at your comment :cool3: just wondering if you missed the fact the cable couldn't be safely isolated due to it been on the DNO supply side of cutout, I think a few factors came into play here.. lack of experience with coupled supplies, complacency and assumption - regardless the OP has just added a valuable lesson to his experience and no doubt he won't make a similar mistake in the future... luckily for himself no one was injured ... had that lead sheath had a bad earth this could have been a whole lot messier but I'm certain after this scare he will have deffo learnt his lesson....

Been there, done it different circumstances but I'm sure there isn't one seasoned spark on this forum who can claim a clean run without these moments. :oops:
 
Last edited:
An electrician died in similar circumstances at the company where I served my apprenticeship. It was a good few years before I started but it was still talked about
 
As mentioned, I've not seen this is 16 years of my time. I have my own business and rarely make mistakes.

Obviously I should of checked if it was live and have learned a valuable lesson :D

just thought I'd share my mishap on here :)
 
As I mentioned, safe isolation just because you think its dead doesnt mean it is. Surely any competant electrician knows this?

Dillb.....If you can honestly say you have never ever balls-ed up with a live cable that you assumed was dead I would be very,very surprised. I have...loads of times. It's quite correct to talk about safe isolation and all that but in the real world I'll wager there's not an electrician who's been around a while who hasn't got it wrong at least once.
 
I would love to see the state of the fuse finder if op can post a pic...

I got it wrong once myself on a job where someone had used coax from a joint box that went down a wall and into a single box that was taped up , just shows you can't take anything for granted..
 
Last edited by a moderator:
I've had mains on coax too, as well as a bit of 4-core CW1293 phone cable run in through the front door frame from near the phone dropwire joint box. And a figure-8 bell wire that definitely went to an ordinary Friedland bell push (it was on the mains side of the tranny).

I knew the OP was going to be about a shared service issue as soon as I started reading the post, and I don't do domestics so I don't meet them either. The clincher was
an old 6mm lead cable
Not a very common thing to find as a final circuit in an ordinary terraced house. They didn't have a lot of 7.2kW showers in the days of lead-sheathed rubber, but of course PILC was bog standard for service cables since the year dot. And taped up too. Lots of things to set the alarm bells ringing!
 
I came across an understairs cupboard light a few years ago wired in bell wire, and the feed was from a light switch just external to the cupboard - no neutral in there though, it was live and earth - straight into the metal wall box terminal.
All of this wiring was hidden behind boarding in the cupboard and I only found it when doing a CU change - switching this light on caused instant RCD tripping as you can imagine. :cowboy:
 
I came across an understairs cupboard light a few years ago wired in bell wire, and the feed was from a light switch just external to the cupboard - no neutral in there though, it was live and earth - straight into the metal wall box terminal.
All of this wiring was hidden behind boarding in the cupboard and I only found it when doing a CU change - switching this light on caused instant RCD tripping as you can imagine. :cowboy:
In some of the mining houses it was common to see loads of additions done in 'shot wire'
 
Reminder ... anyone offended by any post then use the report button ..do not react please!

Can we continue the thread without the slating thank you :)
 
once went to a customer to refit an alarm contact to a new pvc front door. the fitters had done a lovely job and had fitted a nice shiny brass doorbell push button. unfortunately, the 50 year old doorbell was 240V, so when i pressed the push button, the brass button connected with the fixed 240V contact. OUCH.
 
It's because the supply was still live in a partially cut cable that had blown the fault clear... any vibration could have blown it ... front end fusing may be very high ampage ... hence my earlier comment he's lucky no one was hurt and more so he's not in hospital... cutting through a DNO cable at close range with zero PPE doesn't usually end well.
 
DaveOCD’s explanation sounds more plausible. Since hydrogen sulfide and mercaptan gas is highly volatile, power gens decision to evacuate the property appears prudent. :nuke:
 
Dillb.....If you can honestly say you have never ever balls-ed up with a live cable that you assumed was dead I would be very,very surprised. I have...loads of times. It's quite correct to talk about safe isolation and all that but in the real world I'll wager there's not an electrician who's been around a while who hasn't got it wrong at least once.

3 days ago I spent the night with a beautiful woman who I have been getting to know for a couple of months. We slept in the same bed so I thought 'eh up things are looking good'. Unfortunately sleeping and chatting were the only things that were permitted, along with the information that not much else would happen until we were married!!!!!:frown2:

The next morning I cut through a live wire as my mind was a long, long way away from were it should have been! :6:
 
I've had mains on coax too, as well as a bit of 4-core CW1293 phone cable run in through the front door frame from near the phone dropwire joint box. And a figure-8 bell wire that definitely went to an ordinary Friedland bell push (it was on the mains side of the tranny)....

I've see CAT5 cable and ripcord/speaker cable used as LV as well on a few occasions as well.

I think there's always going to be things that catch sparkies out even if they're following safe isolation procedures whether it be a hidden redundant supply that's still live, a supply that's crossed over from a different premises, an unexpected battery DC supply when you're testing for AC isolation or even a UPS that's hidden away somewhere. The problems are more common on control systems where there can be numerous points of isolation for a single panel as well as LV/ELV, AC/DC and modulated AC supplies from VFD's.

Most experienced electricians have developed a certain way of working and doing things in general that reduces the chances of them getting a shock in these cases, it's just little things but they make a big difference. In an ideal world you should never get a shock and you should never destroy your side cutters and that's certainly what we should all be striving for but in the real world, if you never get a shock and you need a new pair of sidecutters every couple of years I'd settle for that.
 
Last edited:
I have seen the led sheethed 6mm used as a back to back feed of the supply in a semi detached, looked just like a bit of 6mm T&E just older and made of led, when I worked out what it was I phone UKPN and they didn't believe me for a while, guess there's not much of it about any more. They came out and dug from the road into the house, seemingly no trench, clever stuff!
 
3 days ago I spent the night with a beautiful woman who I have been getting to know for a couple of months. We slept in the same bed so I thought 'eh up things are looking good'. Unfortunately sleeping and chatting were the only things that were permitted, along with the information that not much else would happen until we were married!!!!!:frown2:

The next morning I cut through a live wire as my mind was a long, long way away from were it should have been! :6:


Kick that one into touch mate, it's even less likely once you are married........:77:
 
Just a quick update, power gen UK went to the property feeding both houses and had to evacuate the property.

Regards,

Mike

So the burning question is, did you offer the damsel in distress a roof over her head for the night, given that it was your fault she was evacuated? :wink:
 
So the burning question is, did you offer the damsel in distress a roof over her head for the night, given that it was your fault she was evacuated? :wink:

Good point ; if he had offered her a roof maybe the day could have ended with a bang....
 
Last edited by a moderator:
Good point ; if he had offered her a roof maybe the day could have ended with a bang....

My money is on he offered his honour, she honoured his offer and all night long he was honour and offer.:biggrin:


I will get my coat...lol
 
Another quick update,

it it turned out the house that was feeding both properties is fed in a lead supply cable!

its strange as the house I'm working in has an old resin cable feeding the property.

so far the supply head has been replaced but the supply cable is still lead??

im guessing the cable is 1950's?

Its been left so im assuming it's not being changed anytime soon as it runs through her living room!

Mike
 
Gents, ALWAYS prove DEAD for yourself and prove DEAD to anyone else working with or you or alongside you.
Never assume, also always prove your tester before and after proving DEAD, may seem like overkill but may just save a life.

In a world where everyone wants a job completed at warp speed, puts all of us under pressure but take your time, and be SAFE.
 

Reply to Today ended with a bang! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Was speaking to a family member recently, he told me his iron recently made a bang and flash as he plugged it in to the socket, and could...
Replies
14
Views
2K
Hi. I'm in the process of getting my qualifications and am taking on some small jobs for family to try and get some experience in. Today I was...
Replies
17
Views
899
Hi guys, I don’t really know where to post this, sorry if it’s in the wrong place. After posting a thread about old lead sheathed cable in my...
Replies
22
Views
2K
I have had my kitchen rewired and plastered. I have had a 6mm t+e on a dedicated 32a circuit for a 60cm electric cooker. In hindsight, had i known...
Replies
11
Views
717
Need to replace an old Vent-Axia extractor fan as the pull chord no longer works. I bought this -...
Replies
19
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock