  1. gazdkw82
    Offline

    gazdkw82 Trainee Trainee Access

    Location:
    leicester
    I'm thinking of getting a torque screwdriver but unsure if it's worth it. Is it a regulation now or just good practice now for connections to be torqued? If so is it just for CU's?
     
  2. RWJ
    Offline

    RWJ 8,330 day wonder Electrician's Arms

    Location:
    East Anglia
    It's not a regulation as far as I'm aware. I haven't bothered myself after our area engineer told us about horror stories of terminals not done up tight enough when using a torque screwdriver.
    While he is happy for us not to need them, so am I!!!
     
    • Like Like x 1
    • Agree Agree x 1
    • Informative Informative x 1
  3. gazdkw82
    Offline

    gazdkw82 Trainee Trainee Access

    Location:
    leicester
    That's my concern. Iv used one on a CU and I was a little surprised when it clicked to indicate it was tight enough. I just thought it highlighted how heavy handed I was
     
    • Like Like x 2
  4. Midwest
    Offline

    Midwest Electrician's Arms

    Location:
    Oxfordshire
    There is not a regulation, as far as I'm aware, that you have to use a torque driver to tighten terminals, but there is reg 134.1.1, .....good workmanship......take account of manufactures instructions, and as most CU manufacturers detail torque settings for MCB's etc, it something to consider.

    I have one and use it on MCB's etc, but I also been known to use my wrist torque settings!

    Issue with them, is they need annual calibration, and without the current manufacturers instructions, how do you know the settings for an older MCB etc?
     
    • Agree Agree x 2
  5. gazdkw82
    Offline

    gazdkw82 Trainee Trainee Access

    Location:
    leicester
    So who does the calibration? Let's say your changing a CU or putting a new circuit in, do you think it's a necessary tool to have?
     
  6. Midwest
    Offline

    Midwest Electrician's Arms

    Location:
    Oxfordshire
    Overtightening can have similar effect as under tightening (incorrect terminology)
     
    • Agree Agree x 2
  7. gazdkw82
    Offline

    gazdkw82 Trainee Trainee Access

    Location:
    leicester
    That's why I'm considering getting one. Iv seen one that goes from 0.8-2.0Nm, is that a large enough range?
     
  8. Midwest
    Offline

    Midwest Electrician's Arms

    Location:
    Oxfordshire
    If you have spare cash, it could be useful. If you haven't, its a luxury. That said, if your CU has 'issues' 'cos you've overtightened it, you could be scrutinised 'cos you haven't a torque driver.

    They'll be some old sweats along shortly, to shoot me down in flames :rolleyes:
     
    • Like Like x 1
  9. Midwest
    Offline

    Midwest Electrician's Arms

    Location:
    Oxfordshire
    • Like Like x 1
    • Useful Useful x 1
  10. MisterE
    Offline

    MisterE Regular EF Member

    Location:
    Stoke-on-Trent
    • Agree Agree x 1
  11. Davisonp
    Offline

    Davisonp Regular EF Member

    Location:
    Amersham
    Business Name:
    Absolutely All Electrical LTD
    I started using mine regularly when a couple of MCB’s I was tightening split as I had over tightened.
     
  12. Davisonp
    Offline

    Davisonp Regular EF Member

    Location:
    Amersham
    Business Name:
    Absolutely All Electrical LTD
  13. gazdkw82
    Offline

    gazdkw82 Trainee Trainee Access

    Location:
    leicester
    Really? So any torque screwdriver will do then?
     
  14. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    bloody things . fit for limp wristed poouufs. if you can't tighten a screw down properly, maybe time for a career change to lawyer/accountant/politician/shelf stacker.
     
    • Agree Agree x 2
  15. gazdkw82
    Offline

    gazdkw82 Trainee Trainee Access

    Location:
    leicester
    it's not about that telectrix, it's about wanting to provide a professional and safe service. No matter how good you think you are, you don't have a torque mechanism in your wrist and I bet you have over or under tightened a mcb before. No ones perfect but we can all try to be
     
  16. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    back to basics. tighten, wriggle, pull. tighten again. beats any fancy contraption going.
     
    • Like Like x 2
  17. SparkySy
    Offline

    SparkySy EF Member

    Location:
    Northamptonshire
    As has been said it's not regulation yet but the Stroma assessment guy said it is good practice and that it is worth doing as then you have a leg to stand on if something goes wrong, at least you have compliance with the manufacturers instructions! I have and use the wiha one, it has the range you need for almost all manufacturers. Is nice to use too
    Sy
     
  18. Midwest
    Offline

    Midwest Electrician's Arms

    Location:
    Oxfordshire
    I've heard he's always doing them off his wrists :)
     
    • Funny Funny x 2
  19. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    we never had these new-fangled talking screwdrivers 50 years ago. and we never had loose terminations either. is it a catch22? the invention of the drivers propagates loose terminals, or is it loose terminals propagate the tools. don't matter a damn now anyway. we fit metal CUs, so poor termination is cured at a stroke.
     
    • Agree Agree x 2
  20. gazdkw82
    Offline

    gazdkw82 Trainee Trainee Access

    Location:
    leicester
    Things change. It was changed before me and there isn't much I can do about it. Some things were probably better back then but a damn sight more has improved over the years.

    I'm new to the industry and I'm trying to work and adhere to what is current and what is going to improve standards.
     
    • Like Like x 1
    • Agree Agree x 1
  21. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    you'll always get tghis banter off us old farts. jeez, it took me years to get used to these new-fangled meters with digtoes read out. kept tapping mine to try and see a needle move.
     
    • Like Like x 2
    • Funny Funny x 1
  22. Midwest
    Offline

    Midwest Electrician's Arms

    Location:
    Oxfordshire
    Yep 50 years ago we moved from newspaper to this;
    upload_2017-7-10_22-5-5.jpeg
     
    • Funny Funny x 3
    • Like Like x 1
  23. gazdkw82
    Offline

    gazdkw82 Trainee Trainee Access

    Location:
    leicester
    It's all good :)

    I just want to be positive and move forward :)
     
  24. Specialist
    Offline

    Specialist Electrician's Arms

    Location:
    South Wales
    Told you Not to have Weetabix for breakfast ;):)
     
  25. Pete999
    Offline

    Pete999 Trusted Advisor

    Top Poster Of Month

    Location:
    Northampton
    You mean stopped using them don't you mate
     
    • Funny Funny x 1
  26. Specialist
    Offline

    Specialist Electrician's Arms

    Location:
    South Wales
    Buying a torque screwdriver won't allow to provide a professional or safe service & if you think buying a torque screwdriver will help you become perfect at the job then God help you.
    Give it a couple of years & they'll no doubt change their minds and say they shouldn't be used.
     
    • Agree Agree x 4
  27. Pete999
    Offline

    Pete999 Trusted Advisor

    Top Poster Of Month

    Location:
    Northampton
    They push trainees into buying torque screwdriver sets during the Part P courses don't they?
     
  28. Midwest
    Offline

    Midwest Electrician's Arms

    Location:
    Oxfordshire
    Pete, you gonna to have to let this Part P thing go :)
     
    • Like Like x 1
  29. Pete999
    Offline

    Pete999 Trusted Advisor

    Top Poster Of Month

    Location:
    Northampton
    Why?
     
  30. Wilko
    Offline

    Wilko Electrician's Arms

    Location:
    Berkshire
    Business Name:
    Wilko Electrics
    In support - I have a torque wrench and I can assure it does not settle the cable like Tel's technique. IMO it protects the MCB from damage but it doesn't guarantee a good connection.
     
    • Agree Agree x 3
  31. gazdkw82
    Offline

    gazdkw82 Trainee Trainee Access

    Location:
    leicester
    Why won't it help me to provide a safer and professional service? It's a way of accurately and consistently measuring whats happening. If not for my own security and peace of mind but for any circumstances where a discrepancy may occur and proof of quality of work is required.
     
    • Like Like x 1
  32. Pete999
    Offline

    Pete999 Trusted Advisor

    Top Poster Of Month

    Location:
    Northampton
    Nothing like the feel of a good old tweak with the driver to make you feel secure, there are some who admit to using an electric screwdriver to make connections:fearful::fearscream:
     
    • Agree Agree x 2
  33. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    i do use one. and it's got torque settings. :p
     
    • Funny Funny x 1
  34. Pete999
    Offline

    Pete999 Trusted Advisor

    Top Poster Of Month

    Location:
    Northampton
    Shock. horror.
     
    • Like Like x 1
  35. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    if you feel comfortable using one, then by all means, that's your preference. same as some like the notches in sidecutters for stripping, some don't.it's all down to persolnal likes.
     
  36. Specialist
    Offline

    Specialist Electrician's Arms

    Location:
    South Wales
    Maybe you need to learn to tighten screws properly with a real screwdriver first, Incorrectly tightened connections are down to the operator not the tool used.
    What's going to happen when your nice little torque screwdriver is in for calibration or won't reach the torque specified by a manufacturer ? Are you going to stop doing the job ? ( Very good old saying: Only a bad workman blames his tools for poor work). I've been doing this c**p for over 40 years & never had a problem with either loose or overtightened screws. Whether that be on CU's or accessories and truth be told I seriously doubt that Pete, Tel or any of the other guys have either.
     
    • Winner Winner x 2
  37. gazdkw82
    Offline

    gazdkw82 Trainee Trainee Access

    Location:
    leicester
    I'm sure your a fine electrician, sure sounds like your the perfect example.

    I have never had any issues with loose or over tightened terminals however I am new to the industry and Iv heard it mentioned before about torque settings and iv also seen a few sparks using them. I was just intrigued.

    I better go and speak with quickfit and tell them to get rid of the torque impact guns and use a socket/wrench and some old fashioned man power. :p
     
    • Like Like x 2
  38. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    as i said before, it's what you personally feel comfortable with.
     
  39. Midwest
    Offline

    Midwest Electrician's Arms

    Location:
    Oxfordshire
    Installed some Hager RCBO's today. Dusted off me torque driver, give it a whirl I thought, prompted by this thread. Read the manufacturers instructions for the torque settings...................................tumble weed............................nothing, didley squat, zilch. So tightened it to a tight thing, then a little more.

    The product data sheet on their web site has the details, not useful unless you got a 4g signal :)
     
    • Like Like x 1
  40. gazdkw82
    Offline

    gazdkw82 Trainee Trainee Access

    Location:
    leicester
    How old is the rcbo? Is it
    New?
     
  41. Midwest
    Offline

    Midwest Electrician's Arms

    Location:
    Oxfordshire
    Better be, or I'll be suing my wholesalers.
     
  42. Midwest
    Offline

    Midwest Electrician's Arms

    Location:
    Oxfordshire
    Errr you go, this might take you mind off things, Part P, schemes and other such
    repugnance’s :)

     
    • Like Like x 1
    • Funny Funny x 1
  43. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    nice, but not a patch on this:

     
  44. Midwest
    Offline

    Midwest Electrician's Arms

    Location:
    Oxfordshire
    Whilst I admire your musical library, it doesn't have quite the same visual impact, N'est-ce pas :rolleyes:
     
  45. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    philistine.
    get a grip on real musical talent.
     
    • Agree Agree x 2
Loading...