Hellmooth

-
Esteemed
Reaction score
609
As the title says, I was called by a company that fix aeroplane parts, they have a machine that is used for testing generators, it's stopped working and I was asked to have a look. I've told them it's way out of my depth and I pretty much don't have a clue, but said I would stop by and get a look at the machine and see if I could find any information out. Had a look and seen that the invertor display panel had ST-CC is open, had a look at the manual and it seems it needs to be closed for it to run, has anyone worked on these before, or know someone that could fix it, I'm in Edinburgh, cheers!
 
Last edited:
As the title says, I was called by a company that fix aeroplane parts, they have a machine that is used for testing generators, it's stopped working and I was asked to have a look. I've told them it's way out of my depth and I pretty much don't have a clue, but said I would stop by and get a look at the machine and see if I could find any information out. Had a look and seen that the invertor display panel had ST-CC is open, had a look at the manual and it seems it needs to be closed for it to run, has anyone worked on these before, or know someone that could fix it, I'm in Edinburgh, cheers!


A quick google says that ST is a terminal on the drive and needs to be connected to CC, which is a common for terminals, for the drive to be released to run.

There will be something connected across these terminals, a relay contact from some part of the process or within the panel, and thats what I would be looking at. Likely that the inverter itself is fine.
 

Reply to Toshiba Tosvert-130 transistor invertor in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

I'll try to make this quick... A month ago the taillights all went out, checked the fuse it was blown and replaced it. A couple day later they...
Replies
2
Views
365
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
754
I am not an electrician but am looking for some advice as to how to fix my sporadic light flickering problem that has come and gone for the year...
Replies
24
Views
2K
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
598
Hi, So I'm trying to understand what's going on with my off-peak electricity supply, as something's wrong with it and I'm trying to determine if...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock