i think it was a deer but may have been a cow, this is war story that was swapped so never seen it first handWould have been fine if the fence posts were taller!
Discuss Totally stumped. Night Storage Heater tripping out MCB, but ok on daytime circuit. in the UK Electrical Forum area at ElectriciansForums.net
i think it was a deer but may have been a cow, this is war story that was swapped so never seen it first handWould have been fine if the fence posts were taller!
I can believe it, it’s the sort of thing a farmer would do as opposed to spending money!i think it was a deer but may have been a cow, this is war story that was swapped so never seen it first hand
why should he shell out for insulated copper when he has an almost infinite supply of steel fence wire?I can believe it, it’s the sort of thing a farmer would do as opposed to spending money!
Haha! There’s a bloke at our place keeps horses (or used to when there was money in them!) He fitted some lights in a farmers barn......his payment?why should he shell out for insulated copper when he has an almost infinite supply of steel fence wire?
bloody farmers...
A classic!this post is now getting like one that flew over the cuckoos nest.
how can 5 sparks not work out were the fault lies .not very good is it .If they've been thorough and the heater checks out, the cabling etc. checks out and it doesn't trip on an MCB in the 24 hour board, really that leaves only one thing... the MCB in the E7 board. Change the one feeding the heater that causes the trips for a new one and see if that solves it.
but all e7 mcbs going at the same time would seem very unlikely, from what i gather they have tried putting the circuit into other mcbs in the e7 board and all have tripped with the troublesome heater/circuitCould it not be (as @Murdoch has also hinted) that it's simply a case of the MCBs in the E7 board are getting a little past it?
7 hours a day running near the limit for extended periods of time is going to have some effect on the bi-metal strip.
If they've been thorough and the heater checks out, the cabling etc. checks out and it doesn't trip on an MCB in the 24 hour board, really that leaves only one thing... the MCB in the E7 board. Change the one feeding the heater that causes the trips for a new one and see if that solves it.
Has this not been tried on the using the other MCB's in the E7 boardCould it not be (as @Murdoch has also hinted) that it's simply a case of the MCBs in the E7 board are getting a little past it?
7 hours a day running near the limit for extended periods of time is going to have some effect on the bi-metal strip.
If they've been thorough and the heater checks out, the cabling etc. checks out and it doesn't trip on an MCB in the 24 hour board, really that leaves only one thing... the MCB in the E7 board. Change the one feeding the heater that causes the trips for a new one and see if that solves it.
faulty fuse change !However, they have now wired it into the day time board and it is not tripping. Has anyone got any ideas as we need to get it wired back into the E7 circuit??
Just noticed...if they are 15amp breakers, the unit is getting on a bit. Are you sure they aren't 16 amp?Pretty sure its a 15amp MCB. The point is the particular heater trips any of the 15 MCB's on the E7 board they put it into (the other night storage heaters don't), but the heater does not trip any of the 15 amp MCB's on the main fuseboard when they wire it to that.
Just noticed...if they are 15amp breakers, the unit is getting on a bit. Are you sure they aren't 16 amp?
Bang on...(pun intended)...was a big old house, turned out to be a PIR buried under ivy and unknown to the householder, what it switched on was also unknown, but a L-E fault on the switched side led to a JB under the floor where the cable with the fault could be disconnected. Testing at the DB was clear, but every night at some point the mcb would pop when the PIR activated. A poxy job to trace that one.is an intermittent lighting fault one that occurs only when switched on but fine if left off. ?
Reply to Totally stumped. Night Storage Heater tripping out MCB, but ok on daytime circuit. in the UK Electrical Forum area at ElectriciansForums.net