Hi there im after some advice, I’m thinking of creating a 5 pitch touring caravan site 32 amps per pitch can use a standard 100 amp supply single phase from my dno.
I need to tell my contact at western Power Distribution how big a supply I need.
Can anyone help.
 
Touring caravan pitches normally have a 16a supply at each pitch. A 100a supply will be adequate at 16a per pitch. You will need to separate the earthing system if the supply is TNCS, and refer to section 7 of Bs7671 as there are strict regulations on caravan site installations.
Thank you for the information, but all the touring caravan owners I know all say they need 32amp supplies.
 
Thank you for the information, but all the touring caravan owners I know all say they need 32amp supplies.

They might like it but don't need it. 16A is standard. Although it doesn't explicity state "no diversity", how 708.55.1.5 reads, "the current rating of the socket outlets shall not be less than 16A" certainly implies that, which makes sense, as the demand from each caravan is likely to be similar at the same times of day/night.

In the OP's position, I'd be inclined to create 4 x standard 16A hookups and 1 x 32A hookup, possibly to a larger plot, to receive a larger caravan with a higher price tag.
 
They might like it but don't need it. 16A is standard. Although it doesn't explicity state "no diversity", how 708.55.1.5 reads, "the current rating of the socket outlets shall not be less than 16A" certainly implies that, which makes sense, as the demand from each caravan is likely to be similar at the same times of day/night.

In the OP's position, I'd be inclined to create 4 x standard 16A hookups and 1 x 32A hookup, possibly to a larger plot, to receive a larger caravan with a higher price tag.
you find most statics normally over load on some sites think they are at home on the range .
 
It is a long time since I had anything to do with touring parks , but the most famous one only supplied 16 amp hook up on their sites .
And true to form they were used to the max .
Touring vans have electric stored hot water and blown air electric heating now too. The demand is higher now so look to be resetting the breakers regularly.
 
Last edited:
How Ya doin' HT ? :D another resurrection of old sparks FFS nice to see you again :cool:
Hi mate, alright, just bloody busy constantly it seems. Doing 60 hour weeks at the minute (on top of studying for my degree) - I went cards in to get back to a 9-5, but fat luck with that! My missus isn't complaining when she sees my pay slip each month at least.
 

Reply to Touring Caravan dno connection in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
843
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
535
Ive been asked about supplying and installing a wifi network across a caravan site, as i fitted one myself years ago at the site i worked on. The...
Replies
6
Views
1K
I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
996
About 15 years ago, after having had a modern consumer unit fitted, and prompted by our electrician, I asked my then energy supplier (Tonik) if...
Replies
25
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock