Discuss TP & N Continuity & Polarity in the UK Electrical Forum area at ElectriciansForums.net

Shpark

-
Reaction score
10
Just practicing for my AM2.

When testing a 3P and N socket, as I understand, R1 to R2 is CPC to any live (L1, L2, L3) to prove continuity, but how do you prove polarity?
 
Fundamentally N-E voltage close to zero = correct "polarity" as then all OCPD are in the line conductors.

However, if you are testing without reference to E then you could verify the voltages are nominally 400V for all 3 L-L options, and nominally 230V L-N for all 3 options.
 
Fundamentally N-E voltage close to zero = correct "polarity" as then all OCPD are in the line conductors.

However, if you are testing without reference to E then you could verify the voltages are nominally 400V for all 3 L-L options, and nominally 230V L-N for all 3 options.
Nice one, cheers ☺️
 
I don't know what they expect in the AM2 exam as I am just following the Experienced worker route myself. In practice however I would also check phase rotation while doing this, if you are using a modern voltage probe there's often a "clockwise" or "right" indicator, it should light between L1 > L2 and L2>L3. It's required under 643.9 so it might be worth making a note of it in case they ask.
 
I don't know what they expect in the AM2 exam as I am just following the Experienced worker route myself. In practice however I would also check phase rotation while doing this, if you are using a modern voltage probe there's often a "clockwise" or "right" indicator, it should light between L1 > L2 and L2>L3. It's required under 643.9 so it might be worth making a note of it in case they ask.
643.9 relates to phase sequence, not phase rotation. GN 3 suggests this may be confirmed by testing in a similar way to testing R1+R2, or by visually confirming the correct colours are in the correct terminals at each point in the circuit.

Polarity testing is a dead test, particularly for initial verification purposes, before the circuit is energised.
 
I might be wrong but my understanding that phase sequence and rotation is the same thing. I don't have a copy of the latest GN3 so perhaps it's changed since amd 3.

I agree that the distribution may have it differently from what you expect, In an industrial or commercial setting, it's common to see the phase sequence corrected/changed at a socket or a contractor.

If it's a circuit with a 3phase socket and a DOL as I expect it to be in the AM2 I would assume it was a relevant point and thus 643.9 would apply but I suppose it says maintained not correct...
 
I think my main point is that phase rotation testing involves live testing, whereas phase sequence testing only involves confirmation of polarity by dead testing and or visual inspection.

So, when installing a new 3 phase socket for example, a phase sequence test must be performed for initial verification, before energising the circuit. Therefore dead testing only. Whereas, an existing 3 phase socket has already been energised, so a phase rotation live test can done.
 

Reply to TP & N Continuity & Polarity in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi Guys, sorry if posting in the wrong section. I am due to start 2391-52 course soon, and there seems to be from what I have found out, a 3 phase...
Replies
6
Views
456
Hi all, hoping for some advice, I’ve recent resit my AM2s after failing on first attempt… I’ve passed all my resit apart from section C just on...
Replies
0
Views
839
Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
481
Hi guys, We’ve had a new CNC Machine from China arrive this week. It came with a monitor and a tower to run the software. The monitor and tower...
Replies
7
Views
815
Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Replies
0
Views
676

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock