Discuss tripping rcd in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
Hi All. I was called out today to a tripped RCD in a domestic split board that not would reset unless the main switch was off. All mcbs off, all phase conductors removed in case of stuck mcb but still no rcd reset unless main swith was off. Any ideas, householder was not prepared for more extensive exploration at Sunday rates. Going back to-morrow.
 
Last edited:
is this both RCD'S? If not i had this once and was a faulty RCD. As soon as voltage was applied it was tripping. Swapped it over and it was ok
 
Hi All. I was called out today to a tripped RCD in a domestic split board that would reset unless main switch was off. All mcbs off, all phase conductors removed in case of stuck mcb but still no rcd reset. Any ideas, householder was not prepared for more extensive exploration at Sunday rates. Going back to-morrow.


No power over night??
 
It can only be a neutral to earth fault but how can there be a fault at the rcd if no circuits are energised?

Your MCBs will generally be single pole, so all your neutrals (and CPCs) will still be connected. It doesn't take much voltage to push 30mA through a N to E or a N to N short.

What's the earthing system?
 
As already stated it will be a N-E fault.......I'm somewhat flabberghasted that as an arms member this isnt something you have come across before.
I'm probably more flabbergasted than you! I inspected the installation today expecting to find the N-E fault we would all expect. All circuits IR tested, no faults. 8 Meg ohms L-E on one ring final circuit but that was all.
The rcd behaved and tested as one would expect when everything was back together. My original question still remains but I will re-phrase it.
Why does an rcd trip when there is no current passing through it?
 
It seems the House Holder has removed a faulty bit of equipment like an Iron, or something, or you have corrected the fault when putting the Neutrals back in the correct RCD places maybe, or did i miss the point LMAO its l8 for my old eyes.
 
It seems the House Holder has removed a faulty bit of equipment like an Iron, or something, or you have corrected the fault when putting the Neutrals back in the correct RCD places maybe, or did i miss the point LMAO its l8 for my old eyes.
No and no! I removed all loads prior to testing and tried every appliance or portable equipment available in the house when finished. All circuits were removed one at a time and replace as found. The installation was fine up to the point the rcd tripped and would not reset even with all line conductors removed, and it is fine again now.
 
Wet joint box somewhere?
8 megs aint good, especially if it is only l-e and not on n-e.
In an occupied and dry house IR should be better.
Have you tested end to end yet?

Boydy
 
No and no! I removed all loads prior to testing and tried every appliance or portable equipment available in the house when finished. All circuits were removed one at a time and replace as found. The installation was fine up to the point the rcd tripped and would not reset even with all line conductors removed, and it is fine again now.

The neutral and earths are still connected though arent they....it stops tripping when you turn off the main switch because you are then isolating the neutral.
 

Reply to tripping rcd in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
833
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
812
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock