If running singles in a non metal cable containment system Biff we industrial sparks tend to use the same sized CPCs as phase conductors, 2.5 phase with 2.5 cpc, 6mm2 phase with 6mms cpc etc, hence my comment about a 10mm2 which did have a bit of jest in the post, as for the 4mm2 in a 10mm2 Twin and Cpc, I have always concidered a 4mm2 small in comparison, I would much prefer a 6mm2 cable, I don't like the CPC less than half the size of the phase conductors, unless metal containment is used, it's all wrong IMO, and to add to it, I would like to see the CPC actually sleaved in twin and CPC cables too, it is just lazy and money pinching to have the CPC bare, Now be a good boy and pick the daylights out of that comment

not much of a challenge old bean , as everthing you just said is at complete odds with using the adiabatic to properly size a cpc with regards to evaluating thermal constraints.
and whats with all this "we industrial sparks" bullcrap ? you must think you're the only non domestic spark or something else grand and deluded.
 
Just trying to get Biff to bite, you have probably ruined it now, and I thought we were in for a Friday night boxing match, ah well were done now, I give in he was right, I will have to start something else going now.

beer + popcorn ready
ding ding round 1.
 
to add to my first post though, although I was Jesting about the 10mm2, I was serious about the 6mm2, I really don't like CPCs less than half the size of the phase conductors, and do believe Twin and Earth cables should have the earths sleaved not bare, okay lets go round one, put them up :dita:
 

Reply to Trunking cable capacity in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Is anyone aware of any galv trunking that is smaller than 50x50. I'm drawing a blank online. I've taken over a job that's used 16mm twin and earth...
Replies
12
Views
857
Ok all, I'm looking at a shower install and need a bit of advice selecting the correct cable for the job. The customer has a 10.5 KW shower...
Replies
7
Views
1K
I'm slowly attempting to upgrade and rewire the house I'm in. Started by doing the consumer unit. Got the dno replacing my cable coming as its way...
Replies
12
Views
4K
Hi folks, I'm installing a 3-ph 32A 60309 socket and just wanted to double check my design calcs are right... The circuit will be part of a 3-ph...
Replies
3
Views
2K
Doing an EICR on a top floor flat recently and run into an issue I often do - which is judging imperial sizes when they are larger than the...
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock