so the N is dangling and there are 1 or more lights switched on. as the circuit is open circuit at the n END, then you will have 0 volt drop across the load, therefore you will get the line voltage on the N.
 
I was shocked as well (not literally) and that's what I thought about the polarity but it still doesn't explain why there is no continuity between the Line and Neutral conductors?
 
if all the lamps are low energy you may not get a direct continuity reading due to the electronics in the lamp, depends on the electronics of the lamp , i am asuming the light switches have been switched on
 
You're reading 240v through a lamp which, if it's say a 60W filament lamp will have a resistance approaching 1k ohm - too high for your continuity tester.
 
a filament lamp will read around 80 ohms cold. still too high for some continuity testers.
 
sounds to me like you have lost your neutral if you have removed the neutral from the board then you will get 230volts on the neutral between the earth and neutral , not a very clever thing to do as you could electricute yourself if you touch it, to test it properly do an r1r2 test to ensure you have good continuity on the circuits then do an r2rn to ensure you have neutral continuity

So even when I remove a neutral from a different circuit in the fuseboard and test between Earth and that neutral the voltage will still be 230v?
 
so the N is dangling and there are 1 or more lights switched on. as the circuit is open circuit at the n END, then you will have 0 volt drop across the load, therefore you will get the line voltage on the N.

Really helpful cheers telectrix, so if there is no load on the circuit (all of the lights are off) will there be any voltage at the neutral?
 
So even when I remove a neutral from a different circuit in the fuseboard and test between Earth and that neutral the voltage will still be 230v?


yes think about it like the lads have said you may not get continuity readings if the light switch is switched on breaker on , lamp in the holder then the 230 volt will run through the circuit back to the neutral bar hence making the circuit , if you disconnect the neutral then it stays positivly charged so you will have 230 volts on the neutral , like i said in my post you need to check the circuits continuity by using the r1r2 , r2 rn formual this will confirm polarity and continuity of the cpc , live and neural conductors
 
sorry mis read your post , dont go removing neutrals from other circuits with the power on you could end zapping your self if all your switches are off then you shouldnt get 230 volt on the neutral thats if you have the correct neutral or if you have a shared neutral you could end up with 230 volts , you could also get a lower voltage reading due to induced voltage
 

Reply to Try and figure this one out!!! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi folks I've just identified as cause of lighting circuit tripping in consumer unit a low volts ceiling light with laride transformer taking in...
Replies
7
Views
289
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi. I'm in the process of getting my qualifications and am taking on some small jobs for family to try and get some experience in. Today I was...
Replies
17
Views
879
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K
Hi, looking for some ideas on this. I went to an address on Tuesday following a storm where property has been struck by lightning. When the...
Replies
3
Views
758

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock