Im at the fuse board and there is a fault with one of the lighting circuits. Cut a long story short when the Live is in the breaker the neutral becomes live aswell.
So I presume its a short circuit, I isolate the power and test continuity between Live a Neutral (My tester is calibrated and I tested on a known source before hand) but there is no continuity between the two!!??
Has anyone.... I mean anyone!!! Got an explanation for this?
 
sounds to me like you have lost your neutral if you have removed the neutral from the board then you will get 230volts on the neutral between the earth and neutral , not a very clever thing to do as you could electricute yourself if you touch it, to test it properly do an r1r2 test to ensure you have good continuity on the circuits then do an r2rn to ensure you have neutral continuity
 
so the N is dangling and there are 1 or more lights switched on. as the circuit is open circuit at the n END, then you will have 0 volt drop across the load, therefore you will get the line voltage on the N.
 
if all the lamps are low energy you may not get a direct continuity reading due to the electronics in the lamp, depends on the electronics of the lamp , i am asuming the light switches have been switched on
 
sounds to me like you have lost your neutral if you have removed the neutral from the board then you will get 230volts on the neutral between the earth and neutral , not a very clever thing to do as you could electricute yourself if you touch it, to test it properly do an r1r2 test to ensure you have good continuity on the circuits then do an r2rn to ensure you have neutral continuity

So even when I remove a neutral from a different circuit in the fuseboard and test between Earth and that neutral the voltage will still be 230v?
 
So even when I remove a neutral from a different circuit in the fuseboard and test between Earth and that neutral the voltage will still be 230v?


yes think about it like the lads have said you may not get continuity readings if the light switch is switched on breaker on , lamp in the holder then the 230 volt will run through the circuit back to the neutral bar hence making the circuit , if you disconnect the neutral then it stays positivly charged so you will have 230 volts on the neutral , like i said in my post you need to check the circuits continuity by using the r1r2 , r2 rn formual this will confirm polarity and continuity of the cpc , live and neural conductors
 
sorry mis read your post , dont go removing neutrals from other circuits with the power on you could end zapping your self if all your switches are off then you shouldnt get 230 volt on the neutral thats if you have the correct neutral or if you have a shared neutral you could end up with 230 volts , you could also get a lower voltage reading due to induced voltage
 
This has to be a college question if not this guy is dangerous. To be fair I did get a belt today off a borrowed neutral it was dead until my mate turned another lighting circuit on not the one I was working on and that's how we found it, and I must say it was a painful one. But this building had a periodic done 8 weeks ago and passed, me thinks they used the magic invisible test kit .
 

Reply to Try and figure this one out!!! in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock