trying to answer a 2394-5 testing question help please

Discuss trying to answer a 2394-5 testing question help please in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

G

guy 73

Q The earth fault loop impedance for three of the final circuits were

L1.1 0.61 ohms
L1.2 0.42 ohms
L2.3 0.21 ohms

determine, showing all calculations, whether these circuits comply with BS7671

the scenario I have stats measured Ze 0.08 all at 20c
do I have to do something with 80% 0.08 rule of thumb ??
 
Guy may I suggest a little Hello from you and maybe a brief description of your qualifications etc, just to help the members Tailor their replies accordingly.
 
As a new user I think your posts have needed to be moderated so are arriving delayed.
Your first post had missing information.
This post does not have enough information for us to answer directly, however you are on the right lines with the rule of thumb. (0.8 not 0.08 btw), the maximum values of EFLI in BS7671 are given for 70°C, Ze is irrelevant in this case as it is part of the EFLI value measured on the three circuits.
 
Richard you're right his first 5-6 posts need to be approved, I will keep my eye on the thread to try and keep it up to speed.
 
Q The earth fault loop impedance for three of the final circuits were

L1.1 0.61 ohms
L1.2 0.42 ohms
L2.3 0.21 ohms

determine, showing all calculations, whether these circuits comply with BS7671

the scenario I have stats measured Ze 0.08 all at 20c
do I have to do something with 80% 0.08 rule of thumb ??

You need to provide the protective device type and rating, so you know which table to look at in BS7671 before you can work out if it is compliant or not.

Cheers...............Howard
 

Reply to trying to answer a 2394-5 testing question help please in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock