Discuss TT 100ma Rcd + earth electrode?? in the Australia area at ElectriciansForums.net

I

impactes

Hi al,l I am working on a tt system at present. I am going to be a adding a new d/b which will be ran from an existing board which has a 30ma main switch, controlling 1 other circuit i need to change the main switch to 100ma and the 1 circuit its controlling will need changing to a 30ma rcbo as its controlling outside power and lights.
The reason i need to change the main switch is because i will be using 30ma rccbs at new db.

The question i need answering is does the 100ma rcd need to be time delayed? If so the problem i have is that its a hager board and cant seem to find a time delayed rcd from them, so is there an alternative manufacture which i will be able to use? or do they do 1 and am i just not looking in the right place?.

Also would it be advisable to put in new earth electrode to supply new d/b current Ra 25.8 ohms.

Cheers
:)
 
The 100mA RCD would need to be time delayed to provide discrimination.

Also the Ra of 25.8 is good so I would be happy to leave as is.
 
Hi sorry to jump back in with another question.
But was just thinking does the cable that i will be running to the new d/b not need to be 30ma protected, as once i change the rcd it will only be 100ma protected.

Many thanks
:)
 
Depends what cable it is and how it's installed. I assumed you'd already taken that into account.

Yeah apologies didn't think till afterwards, was just trying to avoid any nuisance tripping. Its a 16mm T&E and is ran in a boxing (approx 8 metres) straight from existing d/b and then is clipped direct about 600mm to new d/b. I assume from this it will need 30ma protection?.

Your advise is much appreciated
Many thanks
:)
 
Is it at any point buried in the wall i.e chased in and plastered over???

For the 600mm it is clipped direct, to what is it clipped direct to...wall surface???

If it is within a purpose made boxing and surface clipped or in mini trunking then the additional 30mA protection is not required.
 
Is it at any point buried in the wall i.e chased in and plastered over???

For the 600mm it is clipped direct, to what is it clipped direct to...wall surface???

If it is within a purpose made boxing and surface clipped or in mini trunking then the additional 30mA protection is not required.

No it is not chased into the wall and is clipped to the surface. So will be able to change it.

Many thanks
:)
 

Reply to TT 100ma Rcd + earth electrode?? in the Australia area at ElectriciansForums.net

Similar Threads

See this time after time - poor installation: new split load board on a re-wire tt installation. The main switch is not a time delay rcd. The...
Replies
2
Views
316
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
Replies
6
Views
877
Keeping this brief.....................New dwelling.....TT system with 100mA S type rcd protected supply to local board with 30mA RCD. Freelance...
Replies
21
Views
3K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
539

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock