I'm working at a farm with a 3 phase PME supply to a cupboard in the house containing the house CU and two 3 phase isolators feeding SWA cables to other parts of the farm.
There's an earth terminal block connected to the PME connection and the SWA armour and earth cores; but not to the earth terminal on the CU. This may be connected to an earth rod (I've got to confirm this).
Ze at the CU is 5.1 ohms (fine for TT). Ze for the other supplies is 0.22 ohms.

Is there any reason why I shouldn't connect the CU earth to the PME terminal?

Cheers.
Pete
 
Very unusual. A supply company may bring a PME supply into a property but only make a TT supply available for take-off. Maybe somebody before you has connected as PME not know what that the supply was PME


Check with the DNO to see what supply has been made available. If it is TN-C-S the you will have to bring the cu installation up to TN-C-S standards before using the available earth facility
 
Tncs supplies are not generally used for farm supplies,as there are too many complications with bonding. It would be expected that the house CU would be Tncs,and the farm supplies separated...it is possible that the PME has just been used to protect the SWA's and separated at the farm buildings.....Further investigation is required.
 
Hi Guys
As usual your answers have raised more questions!
1. More investigation of SWAs required
2. So I can PME the CU? It currently has a 30mA RCD Main Switch. Would I be expected to upgrade it to a 17th Ed Dual RCD unit?
Cheers
Pete
 
I work on a large house which had tns, tncs and tt all going in a different places. We moved the incoming supply with the local electricty board to incorporate a back up generator and it was then set as a tncs system.
As I see it, it depends on how old the cable is and what work is involved. 3 core pme is cheaper and easier to install; 4 core tns is still available usually on steel buildings where high start-up currents cause problems with RCD's tripping.
TT should always be used on farm buildings and tncs to the farm house if available.
 

Reply to TT and TNCS (PME) at same address! in the Australia area at ElectriciansForums.net

Similar Threads

5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
537
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
582
Afternoon All, Just pricing up a job and thought I'd pick your brains. Quick run-down, Block of Flats with an underground car park. In the...
Replies
27
Views
2K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock