G

graham123

3ph TT supply into hotel. 300ma time delay rcd protecting a square d qox board. No 30ma RCD protection to any circuits including electric showers. Their is signs of supp bonding in some bathrooms. Thoughts on codes for circuits. Normally pme I would of said c3 for sockets not 30ma RCD protected. Unless for outdoor use. And c3 for shower as bonding present. But I seem to recall somome telling me if its TT then a c2 for all circuits
 
A 300ma rcd is not ideal but providing touch voltage conditions are met then fault protection is provided. The 30ma rcd provides additional protection and the earthing system should not be relevant.
 
Is everything else in good condition?
They really should make use of safety updates and I wouldn't want to stay there, but if there is no defect and it complies with an earlier edition (?)
 

Reply to TT coding advice for a hotel in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

See this time after time - poor installation: new split load board on a re-wire tt installation. The main switch is not a time delay rcd. The...
Replies
2
Views
332
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Hello guys n gals, Did n EICR other week in a flat where the shower circuit was 40A mcb with RCD protection, 6mm cable. Only about 10M run. The...
Replies
14
Views
3K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
Another what code! This is in conjunction with an EICR I have just carried out. 9.5kW shower on 6mm and 32A MCB. Been in place for a long time...
Replies
8
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock