Yeah thats my question done with cheers everyone however will connecting the main earth with a metal pipe not require any rcds?
And how to check if the main earth is connected to a pipe instead of a rod.
John
 
Yeah thats my question done with cheers everyone however will connecting the main earth with a metal pipe not require any rcds?
And how to check if the main earth is connected to a pipe instead of a rod.
John

You need an RCD and also an earth connection. I really would recommend getting an electrician in to check this out - it could well be dangerous.

Or, as I said, post a couple of photos - one of your consumer unit and one of what is behind those tiles.
 
Yeah thats my question done with cheers everyone however will connecting the main earth with a metal pipe not require any rcds?

It will still require RCD's for fault protection.

(technically if it is a large amount of buried pipe, which you own, is on your property, has a very low resistance to earth, is protected against being removed or disconnected, doesn't carry any gas or other flammable/explosive fluid and is suitable for use as an earth rod then you may not need RCDs for fault protection. But you would still need RCDs for other types of protection)

And how to check if the main earth is connected to a pipe instead of a rod.
John

Visually, follow the cable and see what it connects to.
 
My concern is that there is apparently considerable uncertainty about whether this installation would disconnect under fault conditions as opposed to sitting there with live metalwork ready to kill someone.
From the questions asked I don’t think we are going to be able to reliably guide the OP to an answer.
This could be a life or death matter and as DPG said the installation really needs looking at asap.

I also wouldn’t want to unduly raise the OP’s hopes about a suitable and compliant earth via pipework as in my experience it’s rare to find compliant examples of this in domestic properties, at least where I live. I slightly regret even mentioning water pipes now as they are almost certain to be a red herring.
 
yes mate can you remove this entire thread, i give up. With this thread it might motivate me in touching the cutout fuse so might aswell remove this thread
 
yes mate can you remove this entire thread, i give up. With this thread it might motivate me in touching the cutout fuse so might aswell remove this thread

Not sure what the problem is here. People have taken time to give you thoughts and opinions. Just open up the tiling and we can see what's there.
 
My concern is that there is apparently considerable uncertainty about whether this installation would disconnect under fault conditions as opposed to sitting there with live metalwork ready to kill someone.
From the questions asked I don’t think we are going to be able to reliably guide the OP to an answer.
This could be a life or death matter and as DPG said the installation really needs looking at asap.


I've seen TT installations where a fault meant live metalwork - not a fun situation.
 
yeah true but the lucky man here got earth leakage circuit breakers, but its kind of disappointing to see that as all the pipes are connected with the earth and under a fault condition not all current flows to the elcb as some goes to the other pipes and most luckily they have lower impedance compared to the breaker.
 

Reply to TT earthing enquiry. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi How do i access the earth rod to service it, where abouts will it be located and does a tt system have upfront rcds which will be probably in...
Replies
3
Views
1K
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
Keeping this brief.....................New dwelling.....TT system with 100mA S type rcd protected supply to local board with 30mA RCD. Freelance...
Replies
21
Views
3K
On a TT system the rcd must operate withing 0.2 seconds for many circuits. Why when we test rcd's does it not say 300ms for TN systems or 200 ms...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock