Discuss TT off water main or tncs with no earth (Victorian house city centre) in the UK Electrical Forum area at ElectriciansForums.net
542.2.6 Dose state that.I was under the impression that you can only use a water pipe of it's your own private supply ..
I was under the impression that you can only use a water pipe of it's your own private supply ..
I was under the impression that you can only use a water pipe of it's your own private supply ..
Yes, it dose.It goes on to say that other metallic water supply pipework should not be used as an earth electrode unless precautions against it's removal and it has been considered for such use.
Thankyou. Here we go again, many questions will follow the path ofYou should keep an eye on the 18th. It has a few things to say about this
Chapter 54
CLICK
That is TNS.The earth block runs into the terminal and there is space for a link, the neighbour's block is identical and has a link- here's the a pic of the next door one...View attachment 41076
The earth block runs into the terminal and there is space for a link, the neighbour's block is identical and has a link- here's the a pic of the next door one...View attachment 41076
If that's the the case and yo've got 37 ohms yo've cracked it any thing under 100 is fine.
For embedded metal work or earth rod ********Where did you get that bit of nonsense from? Direct from the ******** generator at NICEIC headquarters?
Where did you get that bit of nonsense from? Direct from the ******** generator at NICEIC headquarters?
For embedded metal work or earth rod ********
200 Ohms is the value recommended not to be exceeded in regs, as you well kn0w . Yes NICEIC do recommend under 100. For an earth electrode. So far as the nonsense is concerned(I'll be objective here not obstructive)If you look at B.S.7430 IT RECOMMENDS 100 ohms max and 2 meters of rod as the top meter of soil can be unreliable. Eh?Eh? I asked where you got that value from, not what you were referring to.
Not with the current regs,it will not comply.You would have to drive a new earth electrode down.@James Kinrosd. A water pipe can be used with the owners permission .
Reply to TT off water main or tncs with no earth (Victorian house city centre) in the UK Electrical Forum area at ElectriciansForums.net
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.