Discuss TT off water main or tncs with no earth (Victorian house city centre) in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
Hi guys came across this today, Ze of 37 ohms, surprised me as thought it was a tncs- Victorian house, Db from 1989, no docs- could it be a TT off the water main? 10mm bonding to gas and another 10mm out of sight. The met on the rhs of tncs
block not connected to neutral- can anyone help me with some ideas? Cheers.
IMG_20180228_104819916.jpg
IMG_20180228_114411875.jpg
 
Hard to tell from your pic, set up would suggest TT. Have you followed the route of the EC and see where it terminates, the head looks like PME, have you asked the DNO?

Just re-read your post, you say the earth is not connected to the neutral link?
 
Hard to tell from your pic, set up would suggest TT. Have you followed the route of the EC and see where it terminates, the head looks like PME, have you asked the DNO?

Just re-read your post, you say the earth is not connected to the neutral link?
Try to get a PME terminal from the DNO or you could drive a new spike in directly below in the sub floor and convert to tt system,
then sell them a new board.
 
EV disappears below floor to back of house possibly to water main. Rang DNO, they were not helpful- have to wait for an appointment. Earth not connected to neutral- inside the block, seals already broken. Checked neighbour's, his is the same but neutral connected to earth inside the block - looks like his is tncs and he had a 0.54 Zsat the kitchen ring..
 
EV disappears below floor to back of house possibly to water main. Rang DNO, they were not helpful- have to wait for an appointment. Earth not connected to neutral- inside the block, seals already broken. Checked neighbour's, his is the same but neutral connected to earth inside the block - looks like his is tncs and he had a 0.54 Zsat the kitchen ring..
Any sticker on the neighbours? ;)
 
It was common practise many moons ago to use the pipe as means of earthing . You still can with the owners permission which would be a pain to get and unreliable as pointed out,with constant upgrading etc.to plastic

It was common up here as there are a lot of TT systems .
A lot were in the colliery housing areas , the replacement plastic pipes left the old cast pipes intact , usually under the gardens , so fairly safe until the houses are demolished .
The last one I worked on many years ago the RA was 6 Ohms.
 
Many thanks for your replies guys! Even if left as is, or with an additional earth spike, am thinking the board would have to be updated to protect the circuits on the right hand side that only have a 100ma RCD to bring them under a 30ma RCD.....
 
Many thanks for your replies guys! Even if left as is, or with an additional earth spike, am thinking the board would have to be updated to protect the circuits on the right hand side that only have a 100ma RCD to bring them under a 30ma RCD.....
 
It was common up here as there are a lot of TT systems .
A lot were in the colliery housing areas , the replacement plastic pipes left the old cast pipes intact , usually under the gardens , so fairly safe until the houses are demolished .
The last one I worked on many years ago the RA was 6 Ohms.
Innovative more than informative, rus. I like that.
Common sense really, though, as you say.
 
Yes ' The death of common sense ' lol.
The ground was so wet around these houses anyway even with rods the readings were quite good. They are still standing and in use to this day.
Not by Miners though . ( cap intended) :)
 
What is the earthing block to the rh side of the cutout?
The cutout is just one of the solid n e ones which doesn't require a link. That cannot be taken as an indication that PME is available
 
I had a dodgy homemade tns the other week with a Ze in the kilo ohms. DNO came out, officially declared it was never a tns (probably was in reality, should check a few neighbours maybe) and that I should TT it. Very decent initial Ra of 11 ohms from one rod, with a Zs that dropped to 1.35 ohms ish on a B32 with the water bond. I am very tempted to bang another rod in to see if I can bring the Zs's down further, albeit with a lot of thanks to the water supply pipe!
 
It goes on to say that other metallic water supply pipework should not be used as an earth electrode unless precautions against it's removal and it has been considered for such use.
 
Looks like a TNS from a lead covered cable.
Originally supply cables did not provide an earth point the lead just providing protection for the cable, so many services are actually TNS with no earth terminal.
 
The earth block runs into the terminal and there is space for a link, the neighbour's block is identical and has a link- here's the a pic of the next door one...View attachment 41076

That is a TNS cutout fed by a split concentric cable, you can just see the bare earth conductors connected to the earth terminal internally.

However this begs the question of why you are breaking the seals and taking cutouts apart?
 
Eh? I asked where you got that value from, not what you were referring to.
200 Ohms is the value recommended not to be exceeded in regs, as you well kn0w . Yes NICEIC do recommend under 100. For an earth electrode. So far as the nonsense is concerned(I'll be objective here not obstructive)If you look at B.S.7430 IT RECOMMENDS 100 ohms max and 2 meters of rod as the top meter of soil can be unreliable. Eh?
 

Reply to TT off water main or tncs with no earth (Victorian house city centre) in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor...
Replies
5
Views
3K
Afternoon all I am looking for some advice as on what to with the suppliers earth after a conversion to a TT system. Current issue is earthing...
Replies
10
Views
2K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
918

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock