Discuss TT off water main or tncs with no earth (Victorian house city centre) in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
Hi guys came across this today, Ze of 37 ohms, surprised me as thought it was a tncs- Victorian house, Db from 1989, no docs- could it be a TT off the water main? 10mm bonding to gas and another 10mm out of sight. The met on the rhs of tncs
block not connected to neutral- can anyone help me with some ideas? Cheers.
IMG_20180228_104819916.jpg
IMG_20180228_114411875.jpg
 
Hard to tell from your pic, set up would suggest TT. Have you followed the route of the EC and see where it terminates, the head looks like PME, have you asked the DNO?

Just re-read your post, you say the earth is not connected to the neutral link?
 
Hard to tell from your pic, set up would suggest TT. Have you followed the route of the EC and see where it terminates, the head looks like PME, have you asked the DNO?

Just re-read your post, you say the earth is not connected to the neutral link?
Try to get a PME terminal from the DNO or you could drive a new spike in directly below in the sub floor and convert to tt system,
then sell them a new board.
 
EV disappears below floor to back of house possibly to water main. Rang DNO, they were not helpful- have to wait for an appointment. Earth not connected to neutral- inside the block, seals already broken. Checked neighbour's, his is the same but neutral connected to earth inside the block - looks like his is tncs and he had a 0.54 Zsat the kitchen ring..
 
EV disappears below floor to back of house possibly to water main. Rang DNO, they were not helpful- have to wait for an appointment. Earth not connected to neutral- inside the block, seals already broken. Checked neighbour's, his is the same but neutral connected to earth inside the block - looks like his is tncs and he had a 0.54 Zsat the kitchen ring..
Any sticker on the neighbours? ;)
 
It was common practise many moons ago to use the pipe as means of earthing . You still can with the owners permission which would be a pain to get and unreliable as pointed out,with constant upgrading etc.to plastic

It was common up here as there are a lot of TT systems .
A lot were in the colliery housing areas , the replacement plastic pipes left the old cast pipes intact , usually under the gardens , so fairly safe until the houses are demolished .
The last one I worked on many years ago the RA was 6 Ohms.
 
Many thanks for your replies guys! Even if left as is, or with an additional earth spike, am thinking the board would have to be updated to protect the circuits on the right hand side that only have a 100ma RCD to bring them under a 30ma RCD.....
 
Many thanks for your replies guys! Even if left as is, or with an additional earth spike, am thinking the board would have to be updated to protect the circuits on the right hand side that only have a 100ma RCD to bring them under a 30ma RCD.....
 
It was common up here as there are a lot of TT systems .
A lot were in the colliery housing areas , the replacement plastic pipes left the old cast pipes intact , usually under the gardens , so fairly safe until the houses are demolished .
The last one I worked on many years ago the RA was 6 Ohms.
Innovative more than informative, rus. I like that.
Common sense really, though, as you say.
 
Yes ' The death of common sense ' lol.
The ground was so wet around these houses anyway even with rods the readings were quite good. They are still standing and in use to this day.
Not by Miners though . ( cap intended) :)
 

Reply to TT off water main or tncs with no earth (Victorian house city centre) in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor...
Replies
5
Views
2K
Afternoon all I am looking for some advice as on what to with the suppliers earth after a conversion to a TT system. Current issue is earthing...
Replies
10
Views
2K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
890

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock