Discuss TT Submain and switch fuse in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
9
Another question!

I'm designing for a TT system, there's going to be one 10 way Rcbo consumer unit for the house, less than 3 metres away from the DNO cutout, I'm going to swap the main switch with a 100ma Stype rcd to provide fault protection ( I'll be fitting a tails clamp inside the CU and a tails gland on entry into the CU so there is very little risk of a fault but cost is not an problem so I'd rather fit it).

However, there is another consumer unit in a garage about 10metres away, my plan is to run an SWA in to this new board, obviously being TT it will be highly unlikely to meet the Zs values to allow the fault current to blow the fuse, therefore no fault protection. The fault protection will be in the way of another 100ma s type rcd installed next to the house consumer unit.

My question; with it being over 3metres away, should I install a 100ma s type rcd AND an appropriate sized switch fuse? The fault current will never get to the point to blow the fuse but I suppose I'll have to cover overload issues with it (no issue of overload either really).

(I was just going to install a 4 way unit, 2 ways for the 100ma s type and 2 for the switch fuse).

A question regarding the earth rods aswell, although the submain cable run length is about 10metres the earth rods would only be about 3metres apart once installed. Would it be wise to install one earth rod and have the garage consumer unit run off the same earth as the house, or should I install an earth rod each? And maybe even link them?

I am terrible for writing questions and making it clear so I hope you all understand the above.

Cheers
 
your SWA needs overcurrent protection i.e. Sw/Fuse. I would try 2 long rods and lnk them. might give you a better Ra.
 
your SWA needs overcurrent protection i.e. Sw/Fuse. I would try 2 long rods and lnk them. might give you a better Ra.
Yeah that's what I thought. So I think the way I'm going ti do it is the best way, 100ma s type rcd for fault protection and a switch fuse adjacent to it for overcurrent protection.

Yeah I'm going to go with the two rods and link them aswell. Cheers!
 
PSSC should be sufficient to operate the fuse under fault conditions. If the PEFC is too low then an S type RCD would suffice and give discrimination.

So yes to a fuse and yes to an RCD.
 

Reply to TT Submain and switch fuse in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
Hi all, what is the best way to configure surge protection in domestic dwellings when you have multiple consumer units? Does each consumer unit...
Replies
21
Views
4K
Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
Replies
6
Views
875
Hello, Is there an actual age limit on house wiring that would prevent a traditional fuse box being replaced with a consumer unit please...
Replies
8
Views
1K
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock