The size should be determined via the adiabatic equation.
Whilst he may be correct that 16mm is not required, there is no reason to remove it.
It’s TT earthing.
Your not going to get hundreds of amps of fault current flowing in the earthing conductor.
(Depending on Ra) but I doubt it’s any higher than the ccc of 2.5mm single which is why the table exists
Even at 10 ohms Ra that’s only 23 amps of fault current which is never going to blow the service fuse.
 
Hi guys

At a job doing a re wire and the electrician i was with is changing the earth cable over from 16mm to 6mm
He says as its a tt system that it only needs a 6mm.

Is this right?
I think there must be a reason why he's doing this as no one would remove a cable in this scenario just because a smaller cable would be acceptable..... ooops, sorry, 'conductor' :). Tell us more of the story Magnoliafan?
 

Reply to TT system earth cable size....... in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

The electrician that installed my cooker circuit put in 10mm cable with a 32a fuse, a 45a cooker switch and 10mm cable to the backplate for behind...
Replies
23
Views
931
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
760
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Im starting a re-wire of a top floor flat, they have run an 16mm T&E with a 6mm earth from the ground floor to the 3rd floor feeding the CU...
Replies
18
Views
1K
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock