guys,

been to a house this after noon which is on a tt system. Found that the man rcd before the board has a rated tripping current of 500ma was wondering if this is correct as cannot find it in the regs also is it right that you can only do a half reading and a x 1 reading on this unit.(rcd test)

thanks for your help
 
i would seriously consider fitting 30mA RCD protection and utilise that useless junk just as a board isolator. believe current regs. specify 30mA on a TT.
 
Last edited:
don't forget to IR the installation first and allow extra cost if you find any poor readings
 
A lot of TTs going on today....

I'd say if the 500mA is on as an incomer, leave it where it is and install 30mA protection after it. It will be handy as an isolator and could be a good back up. Ideally on a TT I'd want a 100mA incomer and 30mA protection in the board.
 

Reply to tt system rated tripping current of RCD in the Australia area at ElectriciansForums.net

Similar Threads

Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
817
Keeping this brief.....................New dwelling.....TT system with 100mA S type rcd protected supply to local board with 30mA RCD. Freelance...
Replies
21
Views
3K
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock