Big argument with a newly qualified electrician with all the necessary qualifications
Had to give him a hand later on during the day, nice DB fitted &to be fair quite tidy too , with SPD…It’s a TT System with a good Ze 24.8 ohms.
All Rcbo’s except for the Mcb supplying the SPD, which I pointed out to change that for a RCBO..
His argument was it didn’t present a dangerous situation being local to the DB..
My argument it’s a TT system not compliant & a C2
 
Tricky one. The issue with a RCBO feeding it is both the risk it trips on a surge and nobody notices, and also that the sense coil of the RCBO will marginally degrade the SPD's effectiveness.

But the flip-side is with only a MCB you are depending/trusting that the SPD is very VERY unlikely to have a L-E short. That ought to be the case electrically given they are usually MOV L-N and then GDT N-E but it also depends on the internal mechanical layout being such that under serious thermal stress from a nearby lightning strike it won't melt and short out.

If it were me and nobody worrying about the pennies I would have gone for a 100mA delay RCD incomer and then the lowest inductance MCB possible (e.g. 32A D-curve if permitted) or better still one of the SPD that is OK for 100A plus supply fuse so no MCB needed at all. But back in the real world...
 
SPD's should not be downstream of an RCD, the RCD will trip when the SPD starts to dump the surge to earth and the surge protection won't work.

Any SPD fitted to a TT system should be of a type that the manufacturer has approved for use on a TT system.

Whilst his reasoning is incorrect, he is right that an RCD should not be fitted.
 
But the flip-side is with only a MCB you are depending/trusting that the SPD is very VERY unlikely to have a L-E short.

Shouldn't be a problem using an SPD which is designed for a TT system, these will as you have said have protection L-N and N-E so that a failure causes a L-N short and operates the MCB.
An SPD designed only for TN systems will have L-E and N-E protections.
 
SPD's should not be downstream of an RCD, the RCD will trip when the SPD starts to dump the surge to earth and the surge protection won't work.
Strictly speaking it will be the following surge that is not protected. The RCD/RCBO won't have opened in the microseconds/millisecond of the surge that trips it!
 
when the SPD starts to dump the surge to earth
You've got me thinking, and I don't mind looking like an idiot here...
How well can an SPD dump a surge to earth through 24.8 ohms Ze?

In other words, for an SPD to do anything useful at all does there need to be a low impedance earth path?
 
You've got me thinking, and I don't mind looking like an idiot here...
How well can an SPD dump a surge to earth through 24.8 ohms Ze?

In other words, for an SPD to do anything useful at all does there need to be a low impedance earth path?
It reduces the L-N-CPC differences for appliances within the installation so they have much less chance of damage.

I think LPS are usually below 5-10 ohm or so, but also you have to remember as well as keeping the CPC close to "true Earth" 0V they also pull up the local soil to closer, so again it is about keeping the local difference down.
 
What’s the correct SPD for the TT system
They are normally the sort with one device L-N (typically Metal Oxide Varistor) and another device from N to E (typically Gas Discharge Tube). Sometimes this is referred to as '1+1' configuration for single phase, or '3+1' for 3-phase + N supplies, which is confusing as it has nothing to do with 'type 1' (for high energy direct surges) or 'type 2' (for lower energy induced surges). I think the vast majority of devices sold are of that type as it is also suitable for TN systems.

Some suppliers list them by suitable earthing type:

For TN-S and TN-C-S systems you can get alternative configurations where all protective devices are live to E (e.g. L-E and N-E connections). Sometimes this is referred to as '2+0' configuration for single phase, or '4+0' for 3-phase+N. Here is a comparison of two others showing the differing choices:


In most cases the TT style are fine for adequate protection and no need to worry about applicable choice. The TN style can offer lower clamping for voltages to Earth when applicable, but for most electronics what kills them is the L-N difference and you could argue the TT configuration is better for that.
 

Reply to TT System with Upgraded DB/CU in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Pme Swa sub main supplying external tennis courts. Because of cable size,tt system will be installed. The original Pme supply comes from main...
Replies
14
Views
3K
Went to a property today where the lady is having problems with a 30mA rcd tripping during lightning. This is an upfront rcd protecting a small db...
Replies
10
Views
2K
Hi all,just started using this forum,amazed theres so many people on it. I have to change a board on a TT system(haven't done one before). The...
Replies
9
Views
1K
MarkieSparkie
M
T
6MM MAIN EARTH on a tt system with 100 ohm ze at db ,it runs under patio to rod .do i have to upgrade it as it means patio has to come up ? old...
Replies
26
Views
10K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock