Discuss Turning consumer unit on after water damage in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
Hello wise electricians of the world! I am in the UK. Recently we had a water leak which caused some damage in our home, we are currently trying to dry everything out. The water certainly affected at least some electrical circuits (e.g. water was coming through kitchen ceiling spot lights.)

My plan as a homeowner would be, turn off consumer unit, wait until all has dried out, test circuits, turn everything back on. However my contractor is saying according to regs the consumer unit cannot be turned on for 28 days following water damage to the property, indeed he's saying it cannot even be tested. Seems a bit weird to me. Can someone please help me --- under what conditions can we test and reactivate a consumer unit following water damage to the property? To be honest right now I only want to turn on the breaker to the boiler so the CH can go back on.

Thanks in advance :)
 
Ask the contractor to provide the reference number of the reg and the name of the book it comes from.
And say what their trade and or speciality is.

Is this contractor anything to do with an insurance company, do they mean rules / guidance and not Electrical or Building regs?
 
28 days is a new one on me.
A good inspection and test would certainly satisfy, IMO.
I'd also be looking at which circuits have been affected.
We can't tell but you've haven't had a 'river flood', by the sound of things. Has the main supply or distribution equipment been affected?
 
Last edited:
I can see the chicken and egg scenario, you cannot turn on until it is dried out and you cannot dry out using boiler / dehumidifier without power. If it was my house, provided the CU never got wet (if it did, it is scrap) i would disconnect all ccts and wire a temporary cable from the CU to the boiler to get the heating on and perhaps an extension lead from CU for a de-humidifier. Leave it a week or so in this weather and start testing each cct before reconnecting to CU. lighting ccts can be trickier to test as you will need to ensure light switches are in on position and then flip around the 2 way switches to test each leg. Its doable but better to know what you are doing and why.
BTW i did have a similar problem with a leak causing water to come out of a ground floor light switch. After isolating that cct, i stopped the leak but water did continue to appear at the light switch for days after. Eventually i could dry out the backbox and cable and fit a new light switch.
Hope this helps,

Just read above post.. If the incoming supply and meter got wet, i would assume that is/has already been dealt with by energy co.
 
As above. There's certainly no electrical regulation relating to the subject in any way.
Assuming the consumer unit itself has not been affected by water, there's absolutely no reason why any circuit that's away from the affected area and passes an insulation resistance test shouldn't be turned on.
Circuits in the affected area that test OK should be all right to turn on as long as liquid water isn't still dripping, and a bit of common sense is applied.
 
Thanks Snowhead. He is a general building contractor with electricians on staff. He is nothing to do with the insurance company.

Thanks ipf that is helpful, we already got an independent electrician to check insulation resistance is good and that RCDs are working. He reported everything fine so tbh we're not sure what the problem is. But our main contractor is insistent.

Plugsandsparks thanks for your comment. Yes actually we wired in a builders board which we have been using to run dehums/heaters for several days now. So the chicken and egg problem is solved. Now we just want to turn the main circuit board back on.

This advice is really helpful thanks everyone so much. So nobody knows what this 28 day rule could be?
 
If hypothetically speaking there was water damage to the consumer unit would that change the situation? (Bear in mind the unit is currently visibly completely dry and RCDs/insulation resistance has been tested with no problems.)
 
Just think, how many water leakage problems there are every winter, especially in extreme conditions. If there was a 28 day 'dry out' period, people all over the country would have been freezing to death up until a week ago.
 
Possible issue with CU is if water tracking along the cables and then running inside CU. I had a similar issue with a large house with a large DB and a shower leak upstairs caused excessive water to run along the cables, all the way back to the breakers and fill those, eventually ccts started to trip and by the time i arrived, it was a rights old mess, in the end for various reasons, i changed the whole board and breakers.
 
Damp components in the CU would change things completely. A main switch, RCD or MCB that leaks current in the off position would be extremely dangerous to anyone working on the electrics..
Water in the mechanical parts of the MCBS RCDs etc. can also cause corrosion that can cause the mechanisms to seize or the contact parts become high resistance. If water has entered any of the internal parts of the consumer unit they must be replaced.
 
Water in the mechanical parts of the MCBS RCDs etc. can also cause corrosion that can cause the mechanisms to seize or the contact parts become high resistance. If water has entered any of the internal parts of the consumer unit they must be replaced.
Yes, safety critical components, so this is a given.
 
Sounds like 28 days is when his sparky is next available.... If you had a sparks in to do some testing and he was happy, why did he not energize some of the circuits?
 
Agree with all comments I had a call out to a Care Home the other week water damage in the kitchen, water from roof leak.
Disconnected affected fitting checked elsewhere, left with electric on, returning when ceilings are finished refitting new Led VP fittings.
 
Sounds like 28 days is when his sparky is next available.... If you had a sparks in to do some testing and he was happy, why did he not energize some of the circuits?
He did energize and the main contractor is not very happy about that, and I'm stuck in the middle trying to get my facts straight. Thanks everyone what a helpful community.
 
My neighbour had a flood a few years ago, and although the water didn’t run through the CU, just the moisture in the air was enough to damage the breakers.

This didn’t stop the elderly father of another neighbour from turning on the power to give them lights…. Even though water was visibly running down pendant flexes.

First thing I did after the homeowner demanded his insurance company had me do the electrical repairs… was to install a temporary board for dehumidifiers.


I tested every length of cable, and only had to replace metal back boxes, new faceplates, new cabling for additional smoke detectors and a new CU at the end of the job.

Although he had a very good electrician… the joiner, plumber and labourer were idiots.
3 core between two way switches on staircase caught with a plasterboard screw. 3 separate water leaks which resulted in another new heat detector… and a gas leak!


Story over. There is no 28 day limit… but the installation needs tested before energising.
If in any doubt, a temp board can be fitted as soon as possible, leaving all of the installation not energised.

Even if the boiler wasn’t affected, damp could damage the internal board…. Or water got into a remote part of the heating system like a room thermostat. Best to leave it off too.
 
Can someone explain to me why the back box's need changing just because there is some effervescent contamination on them? seems to be padding the job IMO.

Possibly due to partial loss of sacrificial coating?

Had wondered about this myself as they're unlikely to suffer much corrosion if walls are dried out. Obviously if boxes presented evidence of corrosion to steel, for whatever reason, they should be replaced, but that's more likely to be a historic issue than one caused by moisture over the course of a month or so.
 
Can someone explain to me why the back box's need changing just because there is some effervescent contamination on them? seems to be padding the job IMO.

If the galvanised coating of the back box is damaged and the box has started to corrode then it is likely to continue regardless of how dry the wall is at any given moment.

It is sensible to replace everything which has been damaged by the flood.
 
If the galvanised coating of the back box is damaged and the box has started to corrode then it is likely to continue regardless of how dry the wall is at any given moment.

It is sensible to replace everything which has been damaged by the flood.

I took it that Mike's point was related to undamaged boxes, but I guess corrosion could start at knockouts or where fixings have scratched away the coating.
 

Reply to Turning consumer unit on after water damage in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, you all helped me out recently when we had a water leak (mostly in kitchen ceiling), and my landlord's contractor was saying the household...
Replies
7
Views
2K
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
2K
Hi all. Sort of an interesting one. I had a call from a client to say she is getting a shock when using the shower. I told her not to use it and...
Replies
15
Views
2K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
10
Views
769

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock