The chances are pretty slim when all new underground pipes to a house will be plastic these days.

What is CATV?


Coaxial cable, or cable television.

Also phone lines in the US have a shield which are required to be bonded to the service. This provides parellel paths which lower earth Z substantially.
 
A bit late but if curious here is how US homes are served outside major metropolitan areas:


1592643250213.png



1-7 homes on a single transformer. Primary neutral ties in with the secondary neutral. Any phone or CATV is also tied to the secondary neutral at the pole and again at the home.
 
Thanks so the IEC is broken down into quite small publications where as BS7671 includes the whole lot in one publication.
That might be a factor, but I suspect it was originally driven by the desire to save cost of extra PVC and smaller overall size of cable to make installation easier.
This would appear to be the logic behind it.I can appreciate both sides of the argument. Reducing the size of the CPC and not using Insulation for it has obvious economic benefits. On the other side of the equation, a full sized CPC lowers the Fli and allows us to extend the length of the supply cable for cicuits. A full sized CPC will also lower the "touch voltage" appreciably. From an installation point of view the adjustment to full size CPC in T&e cables has been a PAINas as it has knock on effects on the number of cables we can now fit into the standard wavin pipes
 
What about larger circuits in the UK? Circuits over 32 amps? 63amps? 100 amps? 225 amps?
Regulation 543.1.3 suggests the use of the adiabatic equation to compute the minimum size.

But if that is not easy to apply (for example, if the I2t of the source OCPD is unknown) then regulation 543.1.4 has a table which basically has the same earth conductor as the live conductors to 16mm, 16mm for live conductors to 35mm, and then half the live size for conductors above 35mm (rounded up to the next standard size). To illustrate by example:
  • 32A supply on 6mm cable would have a 6mm CPC (larger than UK style T&E which is based on adiabatic limits for standard fuse/MCB, but the norm for 3-core round cables)
  • 100A supply on 25mm or 35mm cable would have 16mm CPC
  • 225A supply on 95mm cable would have 50mm CPC
 
Last edited:
id be more interested (because I hear uk stuff everyday) what the requirement for America are?

You call your CPC - Equipment Grounding Conductors (EGC) ? is that right?
what are the NEC? requirements for the gauge of EGC? your allowed smaller CPC in the USA ? etc
 
id be more interested (because I hear uk stuff everyday) what the requirement for America are?

You call your CPC - Equipment Grounding Conductors (EGC) ? is that right?
what are the NEC? requirements for the gauge of EGC? your allowed smaller CPC in the USA ? etc


Yup- CPC is called "Equipment Grounding Conductor" or "EGC"

Up to 30 amps the EGC is the same size, beyond that it is allowed to be smaller. Table 250.122 determines the size:

View: https://Upload the image directly to the thread.com/MCuYZm0

[automerge]1594377687[/automerge]
There is an exception for motors- a circuit breaker can be upsized by 250%. So 2.08mm2 wire can be placed on a 40 amp breaker.
 
Last edited:
Up to 30 amps the EGC is the same size, beyond that it is allowed to be smaller. Table 250.122 determines the size:
Looking at an example point in that table, 8 AWG is apparently 8.37mm^2 of copper, for a 100A circuit I suspect you are going to hit the adiabatic limit for disconnection times under 5s. So it would need care in the breaker/fuse choice up front and/or Zs at end to make sure nothing serious happens.
 
Looking at an example point in that table, 8 AWG is apparently 8.37mm^2 of copper, for a 100A circuit I suspect you are going to hit the adiabatic limit for disconnection times under 5s. So it would need care in the breaker/fuse choice up front and/or Zs at end to make sure nothing serious happens.


No Zs requirements in the NEC.

Yes, 8.367mm2- here is our AWG to mm2 table:

View: https://Upload the image directly to the thread.com/qsc6YNh
 
Last edited:
Because some countries like to waste the rapidly dwindling natural resources of this planet.
Or maybe they just don't trust the people installing the cables to understand the relatively simple calculations required.
Its not an issue of trust. The calculations speak for themselves. No issue. It's also not about being indifferent about resources. No issue. But speaking from a perspective where I have been using what I might term"British " T&E for most of my career and" Irish" T&E just recently. Obviously I am obliged to use it. But I see it as a trade off. A larger earth allows longer runs due to reduced FLI and volt drop. Touch voltages will be reduced. I have to say I, m also delighted to see the back of all those calculations we had to make for test reports due to the difference in the CSA of L and E in T&E
[automerge]1594414439[/automerge]
Basically you are very unlikely to have an earth rod with an Ra below a couple of ohms, more likely tens of ohms, so under fault conditions the maximum current is in the tens to low hundred Ampere range and for a fraction of a second for the breaker to clear it that is OK. Also most TT installations have an incomer RCD that trips at levels of 100mA to 300mA usually.

So basically you won't see a large enough I2t to overload a 2.5mm conductor.

Having said that, personally I would not use anything below 4mm in that case for mechanical strength even for the protected cases.
[automerge]1594415772[/automerge]
Its not an issue of trust. The calculations speak for themselves. No issue. It's also not about being indifferent about resources. No issue. But speaking from a perspective where I have been using what I might term"British " T&E for most of my career and" Irish" T&E just recently. Obviously I am obliged to use it. But I see it as a trade off. A larger earth allows longer runs due to reduced FLI and volt drop. Touch voltages will be reduced. I have to say I, m also delighted to see the back of all those calculations we had to make for test reports due to the difference in the CSA of L and E in T&E
[automerge]1594414439[/automerge]
Basically you are very unlikely to have an earth rod with an Ra below a couple of ohms, more likely tens of ohms, so under fault conditions the maximum current is in the tens to low hundred Ampere range and for a fraction of a second for the breaker to clear it that is OK. Also most TT installations have an incomer RCD that trips at levels of 100mA to 300mA usually.

So basically you won't see a large enough I2t to overload a 2.5mm conductor.

Having said that, personally I would not use anything below 4mm in that case for mechanical strength even for the protected cases.
[/QUOT
Basically you are very unlikely to have an earth rod with an Ra below a couple of ohms, more likely tens of ohms, so under fault conditions the maximum current is in the tens to low hundred Ampere range and for a fraction of a second for the breaker to clear it that is OK. Also most TT installations have an incomer RCD that trips at levels of 100mA to 300mA usually.

So basically you won't see a large enough I2t to overload a 2.5mm conductor.

Having said that, personally I would not use anything below 4mm in that case for mechanical strength even for the protected cases.
I have seen the minimum size cable for an earth rod go from 2.5 to 4mm to 6mm to 10mm for domestic installations, over the years. Why the change? Soil resistance is still exactly the same as it was decades ago_Obviously the requirement for greater protection through mechanical strength. the current flow under fault conditions remains determined by the rod res (on a good day a 100 ohms?). So under the worst fault conditions there will be max 2 to 3 amps flowing which of course means a 2.5mm is electrically fine (but mechanically not, according to the (our) regs).
I also think that it would unusual to find a, TT Supply system nowadays that does, nt incorporate rcd, s. Though they do exist.
 
Last edited:
Regulation 543.1.3 suggests the use of the adiabatic equation to compute the minimum size.

But if that is not easy to apply (for example, if the I2t of the source OCPD is unknown) then regulation 543.1.4 has a table which basically has the same earth conductor as the live conductors to 16mm, 16mm for live conductors to 35mm, and then half the live size for conductors above 35mm (rounded up to the next standard size). To illustrate by example:
  • 32A supply on 6mm cable would have a 6mm CPC (larger than UK style T&E which is based on adiabatic limits for standard fuse/MCB, but the norm for 3-core round cables)
  • 100A supply on 25mm or 35mm cable would have 16mm CPC
  • 225A supply on 95mm cable would have 50mm CPC

Question...

Why not have the half size option after 6mm2?
 
For example- a table like this in BS7671:

Line Earth
-----------X--------------
1.5mm2=1.5mm2
2.5mm2=2.5mm2
4mm2=4mm2
6mm2=6mm2
10mm2=6mm2
16mm2=10mm2
25mm2=16mm2
35mm2=16mm2
50mm2=25mm2
70mm2=35mm2
95mm2=50mm2
120mm2=70mm2 (50mm2 could also make sense here)
150mm2=70mm2
185mm2=95mm2
240mm2=120mm2
300mm2=150mm2


Although to be frank these numbers would be inconceivable in the NEC- typically the EGC comes out to be about 10-12.5% of the phase conductors.
 
Why not have the half size option after 6mm2?
You can, and that is basically the whole point about the UK-style of T&E cabling having a smaller CPC, simply by:
  • (a) checking the adiabatic limits
  • (b) ensuring it is protected against mechanical damage and corrosion.
Although you can get 16mm T&E in the UK it is rare, typically the biggest you will see in (sort of) common use is 10mm for the likes of large showers or big cookers in a domestic situation.

So the reality is most domestic final circuit wiring in the UK has a reduced CPC and that is fine due to the I2t from MCBs and fuses (when the design is ensuring a disconnection time below 0.4s) satisfying the adiabatic check.

The "half phase size above 16mm" rule is a very basic choice if you are not in a position to validate the I2t that a fault could have. Typically by that size you might be looking at up to 5s disconnection times for a sub-main or main feed cable, and so quite high I2t (even at short times if it is a MCCB that is providing the over-current protection from a source with a very high PFC).
[automerge]1594461357[/automerge]
I have seen the minimum size cable for an earth rod go from 2.5 to 4mm to 6mm to 10mm for domestic installations, over the years. Why the change?
For a typical earth rod you are quite right, no way are you going to roast even 2.5mm on a fault on a TT system, so going to 4mm or more would only be for mechanical strength I guess.

Where the UK has a higher earth bond conductor requirement is for TN-C-S where it might be bonding to a shared water pipe or gas pipe, etc, and in a PME fault case could be seeing high tens (or possibly hundred-ish) of amps flowing as all of the unbalanced neutral currents in that section try to use whatever route the can get home by.
 
Last edited:
You can, and that is basically the whole point about the UK-style of T&E cabling having a smaller CPC, simply by:
  • (a) checking the adiabatic limits
  • (b) ensuring it is protected against mechanical damage and corrosion.
Although you can get 16mm T&E in the UK it is rare, typically the biggest you will see in (sort of) common use is 10mm for the likes of large showers or big cookers in a domestic situation.

So the reality is most domestic final circuit wiring in the UK has a reduced CPC and that is fine due to the I2t from MCBs and fuses (when the design is ensuring a disconnection time below 0.4s) satisfying the adiabatic check.

The "half phase size above 16mm" rule is a very basic choice if you are not in a position to validate the I2t that a fault could have. Typically by that size you might be looking at up to 5s disconnection times for a sub-main or main feed cable, and so quite high I2t (even at short times if it is a MCCB that is providing the over-current protection from a source with a very high PFC).
[automerge]1594461357[/automerge]

For a typical earth rod you are quite right, no way are you going to roast even 2.5mm on a fault on a TT system, so going to 4mm or more would only be for mechanical strength I guess.

Where the UK has a higher earth bond conductor requirement is for TN-C-S where it might be bonding to a shared water pipe or gas pipe, etc, and in a PME fault case could be seeing high tens (or possibly hundred-ish) of amps flowing as all of the unbalanced neutral currents in that section try to use whatever route the can get home by.


Alright- good info! :)

Regarding the last part- I think its time the UK goes back to TN-S.
 
But speaking from a perspective where I have been using what I might term "British" T&E for most of my career and "Irish" T&E just recently. Obviously I am obliged to use it. But I see it as a trade off. A larger earth allows longer runs due to reduced FLI and volt drop.
The volt drop is unchanged by the larger CPC size, only the fault Zs is lower so you may be able to get a longer run in some case.

But the reality is few final circuits are limited in distance by the R2 value. A quick look over the example cases from the On-Site Guide Table 7.1(i) shows the distances limited in most cases by volt drop in the "RCD" column (where Zs is not significant) and when the FLI kicks in (in the no RCD cases).

If you are looking at B-curve MCBs and the TN-C-S upper example Ze values then practically none of the circuits distances are limited in any real sense by Zs (and thus R2 from the CPC size).

In the TN-S case you do see distance limitations come in as the Ze = 0.8 ohm assumption starts to eat in to the R1+R2 allowed to meet the OCPD device Zs, same as the use of C-curve MCB would cause problems on distance by lowering the Zs requirement.
 
If! you can just meet Ze on a TT to provide ADS a CPC of the same size is beneficial instead of just relying on RCD protection.
Yes, meeting on ADS is better than relying on RCD!

But the elephant in the room (or outdoors, typically) is the earth rod. To get OCPD-based disconnection on even a 6A B-curve MCB needs Zs <= 7 ohm. You will struggle to achieve that with a rod or two or three in most soil conditions.
 
Sounds like a debate... I was told TT needs to follow FLI, but not sure of what number to assume for earth rod/supply impedance in the calcs.
In the UK for a TT supply the rod has to be below 50V at the trip current, and to be low enough to be considered "stable".

So for 30mA and 100mA incomers the limits are not the 1667 or 500 ohm, but 200 ohm (considered as "stable"). For RCD above that it is the value computed (so 300mA requires 167 ohm or less rod impedance, 1A needs 50 ohm, etc).

For domestic systems the most common incomer is probably a 100mA delay type RCD, then 30mA ones for final circuit protection. For bigger systems (e.g. farms, etc) you may see 300mA and possibly 1A or 5A for big systems using MCCB-style incomers. At that point the earth electrode impedance is quite low and so you need multiple rods or a significant steel structure that is in contact with the Earth (probably via conductive concrete foundations) to meet it.
 
Alright- good info! :)

Regarding the last part- I think its time the UK goes back to TN-S.
I would give 100% support to the view that the "the UK should go back to TN-S". And would quickly follow that up by saying every other country should follow their lead. We (here in Ireland) have adapted much that is good from the UK, but unfortunately the TN-S supply system never arrived. It is without doubt the "Rolls Royce" of Electrical supply systems.The TNC-S is, in my opinion the "poor relation"
[automerge]1594497207[/automerge]
The volt drop is unchanged by the larger CPC size, only the fault Zs is lower so you may be able to get a longer run in some case.

But the reality is few final circuits are limited in distance by the R2 value. A quick look over the example cases from the On-Site Guide Table 7.1(i) shows the distances limited in most cases by volt drop in the "RCD" column (where Zs is not significant) and when the FLI kicks in (in the no RCD cases).

If you are looking at B-curve MCBs and the TN-C-S upper example Ze values then practically none of the circuits distances are limited in any real sense by Zs (and thus R2 from the CPC size).

In the TN-S case you do see distance limitations come in as the Ze = 0.8 ohm assumption starts to eat in to the R1+R2 allowed to meet the OCPD device Zs, same as the use of C-curve MCB would cause problems on distance by lowering the Zs requirement.
Hi Pc1966, You are absolutely correct that the volt drop is unchanged by the size of the CPC.Funny thing is, it was the first thing that came into my head waking up this morning. Second thing was, "don't post at 10pm on a Friday"..
 
Last edited:
I would give 100% support to the view that the "the UK should go back to TN-S". And would quickly follow that up by saying every other country should follow their lead. We (here in Ireland) have adapted much that is good from the UK, but unfortunately the TN-S supply system never arrived. It is without doubt the "Rolls Royce" of Electrical supply systems.The TNC-S is, in my opinion the "poor relation"

TN-C-S is basically post war recovery much like ring mains. The world today is wealthier than ever having having no excuse to spare raw materials to such a degree.
 
In the UK for a TT supply the rod has to be below 50V at the trip current, and to be low enough to be considered "stable".

So for 30mA and 100mA incomers the limits are not the 1667 or 500 ohm, but 200 ohm (considered as "stable"). For RCD above that it is the value computed (so 300mA requires 167 ohm or less rod impedance, 1A needs 50 ohm, etc).

For domestic systems the most common incomer is probably a 100mA delay type RCD, then 30mA ones for final circuit protection. For bigger systems (e.g. farms, etc) you may see 300mA and possibly 1A or 5A for big systems using MCCB-style incomers. At that point the earth electrode impedance is quite low and so you need multiple rods or a significant steel structure that is in contact with the Earth (probably via conductive concrete foundations) to meet it.

Alright- but don't you still have Line to Neutral impedances to worry about in regards to breaker clearing time?

Also to add- what would my maximum allowed Ze be for a 133/230Y system? That of a TN-S?

1594497998034.png
 
Last edited:
if we look at this touch voltage theory

although not really used today a same size CPC does seem to reduce touch voltage better the a smaller CPC obviously - finding info on Earthing and touch voltages in nearly impossible, over shadowed by ADS there is also a good Irish paper on touch voltages.

Also on TT systems with high Ze same size CPC is beneficial.
"Finding info on earthing and touch voltages is nearly impossible". You write what I think. I would tweek it slightly to finding "accurate info". Firstly, as OC says below the resistance of the CPC in a TT system is largely immaterial. It only really comes in to play in a TNC-S
system. Reason being that in a line to earth fault in a TT system, almost the entire voltage will drop across the rod due to its relatively much higher resistance in relation to the L and the E. The "touch voltage" will thus be largely determined by the resistance of the rod rather than the CPC. However your thoughts about the same fault in a TNC-S system are valid. As the fault current flows, not through the rod, but back through the Neutral, the resistance of the Cpc now plays a much more significant role in determining the "touch voltage". Now, having "put my foot in it" by posting to late on a Friday evening I want to avoid doing it again on a Saturday. I wish you all a good weekend.
 
Alright- but don't you still have Line to Neutral impedances to worry about in regards to breaker clearing time?

Also to add- what would my maximum allowed Ze be for a 133/230Y system? That of a TN-S?
Not sure what the HV transformer picture is for!

Yes, the line-neutral impedance matters but generally speaking if you meet the voltage drop limit of, say, 5% then your PSSC is going to be at least 20 times the nominal current. That is usually going to result in 5s or less disconnection time.

If that is violated then you are looking at longer fault times and so both a higher exposure time to potentially dangerous touch voltages (if it also applied to the earth loop impedance), but also a higher fire/cable damage risk as the I2t is going to be huge due to the large 't' involved.

So back to the Ze value - it should be ideally enough to achieve the disconnect times. For a TN system you need the PFC to be broadly comparable to the PSSC demands from volt drop for that, but you don't want it very high as that can lead to issues in conductor damage, OCPD failure, etc. So some systems have neutral impedances included to limit the PFC to a sane value to allow differential relays to clear faults, allow end circuits clearing, etc, without a risk of damage.
 
Last edited:
Not sure what the HV transformer picture is for!

Just that 138/240Y exists :p A while back several members expressed skepticism that such a system was in existence being that it is not common Europe.

Yes, the line-neutral impedance matters but generally speaking if you meet the voltage drop limit of, say, 5% then your PSSC is going to be at least 20 times the nominal current. That is usually going to result in 5s or less disconnection time.

Good to know.

If that is violated then you are looking at longer fault times and so both a higher exposure time to potentially dangerous touch voltages (if it also applied to the earth loop impedance), but also a higher fire/cable damage risk as the I2t is going to be huge due to the large 't' involved.

Question though- isn't line and neutral such that it is impossible to melt the insulation no matter how high the L-N loop? My understanding is that a circuit breaker's bi-metal will cover and all over load conditions.

Melting is only a concern for line to earth faults with a reduced sized CPC.

So back to the Ze value - it should be ideally enough to achieve the disconnect times. For a TN system you need the PFC to be broadly comparable to the PSSC demands from volt drop for that, but you don't want it very high as that can lead to issues in conductor damage, OCPD failure, etc. So some systems have neutral impedances included to limit the PFC to a sane value to allow differential relays to clear faults, allow end circuits clearing, etc, without a risk of damage.

In no disagreement.

Question- does the UK have series combination ratings? An example would be a 22kaic main breaker and a 10kaic feeder breaker where both will "see" 22,000 amps during a fault. This is allowed on the idea that the manufacturer has tested both breakers such that a fault over 10,000amps will cause both breakers to trip instantaneously.
 
"Finding info on earthing and touch voltages is nearly impossible". You write what I think. I would tweek it slightly to finding "accurate info". Firstly, as OC says below the resistance of the CPC in a TT system is largely immaterial. It only really comes in to play in a TNC-S
system. Reason being that in a line to earth fault in a TT system, almost the entire voltage will drop across the rod due to its relatively much higher resistance in relation to the L and the E. The "touch voltage" will thus be largely determined by the resistance of the rod rather than the CPC. However your thoughts about the same fault in a TNC-S system are valid. As the fault current flows, not through the rod, but back through the Neutral, the resistance of the Cpc now plays a much more significant role in determining the "touch voltage". Now, having "put my foot in it" by posting to late on a Friday evening I want to avoid doing it again on a Saturday. I wish you all a good weekend.


From what I've learned from US forums would be that bonding brings everything to the same potential. A fault on a TT supply practically raises all rebar, water pipping, fittings, appliances ect to 230 volts making for zero volts between the faulted object and everything else inside the building.

The danger being if one where standing outside on remote earth. 230 volts in hand zero volts on earth... so the RCD must operate rather fast.
 
Just that 138/240Y exists :p A while back several members expressed skepticism that such a system was in existence being that it is not common Europe.
Ah!

It is not my area, but I think the UK has mostly delta primary and star (Y) secondary, certainly for the LV final it will almost certainly be a star-connected transformer secondary.

Question though- isn't line and neutral such that it is impossible to melt the insulation no matter how high the L-N loop? My understanding is that a circuit breaker's bi-metal will cover and all over load conditions.

Melting is only a concern for line to earth faults with a reduced sized CPC.
It depends.
In (almost) all cases a circuit has to be protected against a fault (i.e. short) but for some cases it need not be protected against an overload.

For example, a fixed load like a shower, or a sub-min that has a limited load by virtue of the sum of breakers, may have an OCPD that will meet the cable's adiabatic limit in a fault but is not going to stop it melting on an overload.

However, for the majority of cases the OCPD is sized for cable protection so then you would be right, that no matter what the fault current level it would save the cable even if it did not meet the disconnection times expected for shock protection.

Question- does the UK have series combination ratings? An example would be a 22kaic main breaker and a 10kaic feeder breaker where both will "see" 22,000 amps during a fault. This is allowed on the idea that the manufacturer has tested both breakers such that a fault over 10,000amps will cause both breakers to trip instantaneously.
Again it depends, but generally as most MCB/MCCB used here are energy-limiting then you will see "cascading values" in technical data from the manufacturers on what the upstream PFC can be for a combination of devices.

Usually it is a MCB/RCBO that is the downstream device (typically for final circuits below 63A or so), and a MCCB or fuse that is the upstream device (typically the protection for a sub-main or board incomer). The results are not always what you might expect, as if the upstream let-through gets too high you end up limited by the small downstream device's rating.

As an example that just happens to be based on my current project, a 100A BS88 fuse feeding the Hager NBN series of MCB (15kA break limit), for 6A and 10A MCBs the cascaded PFC limit is the 15kA of the MCB, but for the 16A and above MCBs the limit is the 80kA of the fuse.

Why you might ask? Well if you look further down through the Hager data you will find the 6A & 10A have total selectivity with that fuse, so basically they do all of the fault current interrupting, but at 16A the MCB/fuse selectivity limit is 13.6kA thus by time you reach the MCB's PFC limit of 15kA the BS88 fuse is already blowing and limiting the peak fault current and so protecting the MCB from an explosive ending.
 
"Finding info on earthing and touch voltages is nearly impossible". You write what I think. I would tweek it slightly to finding "accurate info". Firstly, as OC says below the resistance of the CPC in a TT system is largely immaterial. It only really comes in to play in a TNC-S
system. Reason being that in a line to earth fault in a TT system, almost the entire voltage will drop across the rod due to its relatively much higher resistance in relation to the L and the E. The "touch voltage" will thus be largely determined by the resistance of the rod rather than the CPC. However your thoughts about the same fault in a TNC-S system are valid. As the fault current flows, not through the rod, but back through the Neutral, the resistance of the Cpc now plays a much more significant role in determining the "touch voltage". Now, having "put my foot in it" by posting to late on a Friday evening I want to avoid doing it again on a Saturday. I wish you all a good weekend.
From what I've learned from US forums would be that bonding brings everything to the same potential. A fault on a TT supply practically raises all rebar, water pipping, fittings, appliances ect to 230 volts making for zero volts between the faulted object and everything else inside the building.

The danger being if one where standing outside on remote earth. 230 volts in hand zero volts on earth... so the RCD must operate rather fast.

Probably should have started a new tread for this as I've been banging on about it for a while but when I'm thinking touch voltage I'm thinking like the pictures below like we were taught at school - Grounding/Earthing an Appliance just having a path of least resistance not your body but the earth/ground/cpc etc bringing it to earth potential but where could you find calculation for this kind of thing? it must make a difference the size of the CPC etc.



Physics.png
Physics (2).png
 
Probably should have started a new tread for this as I've been banging on about it for a while but when I'm thinking touch voltage I'm thinking like the pictures below like we were taught at school - Grounding/Earthing an Appliance just having a path of least resistance not your body but the earth/ground/cpc etc bringing it to earth potential but where could you find calculation for this kind of thing? it must make a difference the size of the CPC etc.



View attachment 59419View attachment 59420

That article is not only wrong and obfuscating, but it is dangerous. Who is it aimed at? :eek: :eek: :oops:
 
Hmm not sure there are several American web sites on the subject and I'm not sure it's wrong

Two examples

1) A Metal case appliance has a fault -Line to the metal case you touch this you are the path to earth through you feet, what happens?

2) A Metal case appliance has a fault -Line to the metal case, but the case is earthed.
You touch this - does electricity flow throw you to earth or does it take the path of least resistance the the Earth\CPC ?
 
Last edited:
Hmm not sure there are several American web sites on the subject and I'm not sure it's wrong

Two examples

1) A Metal case appliance has a fault -Line to the metal case you touch this you are the path to earth through you feet, what happens?

2) A Metal case appliance has a fault -Line to the metal case, but the case is earthed.
You touch this - does electricity flow throw you to earth or does it take the path of least resistance the the earth?

The path of least resistance is the main bonding jumper. Earth has nothing to do with opening a breaker or fuse.
 
Cookie, could you clarify what you mean here.


Here is a visual describing the terms from NEC land:

1594582979667.png



The main bonding jumper is a wire, screw or busbar which connects the equipment ground bar to the neutral bar in the main service equipment. It is mandatory under the NEC as TT earthing is not allowed. The majority of fault current will travel through the bonding jumper onto the neutral bar returning via the utility neutral.


System bonding jumper is a term used for separately derived systems like a transformer or generator.
 

Reply to Twin and Earth CPC in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Morning All, Think I'm having a brain fart but I have a 70mm2 4 core SWA with a separate 35mm2 CPC. Earthing is TNS with main bonding...
Replies
5
Views
1K
I see they're introducing a new type of flat twin cable with a sheathed CPC. In my location there's no requirement to sleeve CPC/bonding...
Replies
21
Views
2K
Good evening all, Some help with following would be much appreciated. A 20 Amp rcbo in a CU supplies an adaptable box on the outside wall of a...
Replies
17
Views
16K
My assessor said that the minimum CSA for a Main earthing conductor for a TT was 16mm. I questioned this as I thought it was 4mm. Regulation...
Replies
30
Views
11K
Hi all, first post, and it relates to quite a challenging installation. The short version is that I'm working through remedial work on a 75 page...
Replies
13
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top