Discuss Two 32amp outlets on one circuit in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

A

AdamKerr88

Anybody got any thoughts on this;

I've been asked to install a new 16 amp 4 pin 415v industrial socket in a workshop to supply a lathe.....seams like an easy request, however there isnt a single distribution board in the building with a spare single phase, let alone a three phase way left on it !

There is another 32 amp 3P socket outlet in the room adjoining the area, this is used rarely, however they wish to keep it where it is for now. I've looked at the options of installing a small 4 way 3P DB next to the existing DB to supply these sockets but again no room and of course no budget for this.

Providing the protective device is suitable to protect the cable installed, i.e 32amp, would it be ok to feed the new 16 amp outlet from the same circuit by taking a SWA from the isolator above the existing outlet to the new outlet and installing a unit with a 16 amp 3 pole protective device above it to protect the outlet at 16amps as required and of course re-identifying the circuit at the DB.

There is next to no chance the two outlets will ever be used at the same time and i cant personally think of a reason why this wouldnt be ok however i've not seen it done before and theres usually a good reason for that.

Any thoughts would be much appreciated.
 

Reply to Two 32amp outlets on one circuit in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi guys I have some industrial lighting circuits to wire in a workshop and was after some fresh ideas/suggestions as to how i could best do this...
Replies
12
Views
1K
I have just had my kitchen redone and the kitchen rewired with a new 6mm cable installed for an electric cooker. However I have changed my mind...
Replies
10
Views
2K
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
671
I'm moving a socket installed on a lighting circuit (installed by previous owner who was a professional electrician so I assume he knew what he...
Replies
7
Views
1K
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
591

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock