Not actually guidance is clear in BS5839:6
... which states that (for Grade D systems):

The mains supply to the smoke alarms and heat alarms should take the form of either:
  1. an independent circuit at the premises’ main distribution board, in which case no other electrical equipment should be connected to this circuit (other than a dedicated monitoring device installed to indicate failure of the mains supply to the smoke alarms and any heat alarms); or
  2. a separately electrically protected, regularly used local lighting circuit in which case there should be a means for isolation of the smoke alarm(s) from the lighting circuit (e.g. for maintenance)
For Grade E systems, (2) is recommended.
 
I'm not really sure. But there's a note underneath the above that says:

This does not imply that there need be separate electrical protection of the smoke alarm circuit; a single means of protection against overload or short circuit (e.g. a fuse or miniature circuit breaker) serving the entire circuit is acceptable.​

Perhaps they're trying to distinguish "proper" lighting circuits from those derived from (switched) fused spurs? Not really sure, though, sorry.
 
I would say that this means that it is acceptable to run smoke detectors on the same circuit as the lighting. But not two circuits, one for smokes and one for lighting, (2 cables) lumped together in one OCPD.

There should also be a means of isolating the smokes from the lighting, ie a switch or FCU.

In fact neither 1 nor 2 in the post before the last suggest that two cables in one OCPD is acceptable.
 
There should also be a means of isolating the smokes from the lighting, ie a switch or FCU.
There is a further note (they just keep coming, don't they?!):

A number of manufacturers use a fixed base for the electrical connections, and the smoke or heat alarm can be readily removed by use of a tool operated release tab, etc.​
 

Reply to Two 'Circuits' in one MCB in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi all, First post here, hope I'm compliant with the rules! I did do a quick search before asking this, but I couldn't quite come up with the...
Replies
3
Views
3K
Hi guys, I've gotten AI to write up a terms and conditions for my company and then went through it with AI and tweaked it to make it sound a...
Replies
3
Views
443
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
899
I installed outdoor lighting and outlets. I finished this past year. I passed my inspection on April 2022. I was so pleased, BUT now the circuit...
Replies
3
Views
923

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock