Discuss two new consumner units from existing supply in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

I

ianbrookes

any advice would be gratefully accepted.

I have two new consumer units to fit, one for a garage supply (2 circuits 20amp and 6amp) and one for a conversion over the garage (4 circuits, 1 32amp, 1 16amp, 2 6amp). I am going to alter the existing meter config (additional tails tails to a block) to allow for an SWA cable to run to the garage which will feed both the new circuits. I am assuming I need a fused safety disconnect switch in the garage and then feed the two consumer units from that (one in the garage one one above in the conversion). any ideas what the best way to do this would be ? and what are the best equipment to use ? thanks in advance.

effectively I want to change an existing single phase supply at the meter to feed two other consumer units.
 
Yes. the main house has a 100amp incomer and 10 circuits, so I wanted to come straight from the meter rather than alter the existing fuse board.
thx.
 
so 2 more boards with a total 86A and the main house with 10 circuits all from a 100A fuse,some calculations needed here i think or maybe another separate supply from the local DNO.
 

Reply to two new consumner units from existing supply in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi guys, I have supplied my Shed with a 6mm SWA cable into a nice consumer unit. In there I have a 6Amp MCB for the lights and a 16 A supplying a...
Replies
25
Views
963
I wondered if it is OK to have 2 x Main Switches in the same consumer unit. One feeding the RCBOs in the House and one feeding the CU in a garage...
Replies
16
Views
753
can anyone please advise on where the wires go? My electrician installed a new cable ready for when I bought a security light. The cable as shown...
Replies
3
Views
546
Hi All I'm new here. I have just finished my NVQ and waiting to do my AM2. I have a question on selectivity as it has always slightly confused me...
Replies
5
Views
749
Hi all, what is the best way to configure surge protection in domestic dwellings when you have multiple consumer units? Does each consumer unit...
Replies
21
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock