Discuss Two Ovens, One Cable in the UK Electrical Forum area at ElectriciansForums.net

Electron

-
Arms
Reaction score
20
As my customer didn't know what double oven they wanted I installed a 40A MCB and 6mm twin and earth. When I returned for the second fix they have installed two ovens. One is a single oven (3.65kw 16A) and the other is a microwave/grill/oven (3.45kw 16A). So what is the best way to connect both with one supply? The first idea I had was to use a 45A DP Switch and wire both ovens to this. Ideally, I would like to isolate each one separately. Has anyone any suggestions?
 
I tend to wire these on a socket and plug top (single socket for each) as one you apply diversity the loading usually drops to below 10amps. Don't know what model you have though could be a particular large single oven ??????? This would mean some kind of joint as sockets won't take two 6mm obviously lol
 
I tend to wire these on a socket and plug top (single socket for each) as one you apply diversity the loading usually drops to below 10amps. Don't know what model you have though could be a particular large single oven ??????? This would mean some kind of joint as sockets won't take two 6mm obviously lol
MK sockets will allow x2 6mm cables
 
I must say I had exactly this situation a few weeks ago, and I put 2 DP switches off the single 6mm cable, one for each oven. However, afterwards I thought it was probably unnecessary, and as Murdoch says a single switch is fine. You have to consider what the switch is for, it only to turn the oven off in an emergency. If one of them fails an electrician will have to disconnect it properly anyway, they are just switches not isolators.
 
Hi Simon - agree above - one switch and a double outlet gets my vote :)
45 Amp Dual Appliance / Cooker Outlet Plate - https://www.tlc-direct.co.uk/Products/AA45DCOP.html

IMG_0778.JPG
 
I take your point but would like to add would never use a plug and socket on anything like a hob or double oven ect just single ovens and combination microwave as these tend to either come with a plug or a piece of 1.5 flex fitted.
Don't wanna sound like a --- but am new here and don't you guys thinking I'm some kinda cowboy yey haw lol
 
I take your point but would like to add would never use a plug and socket on anything like a hob or double oven ect just single ovens and combination microwave as these tend to either come with a plug or a piece of 1.5 flex fitted.
Don't wanna sound like a --- but am new here and don't you guys thinking I'm some kinda cowboy yey haw lol

Too late Rob. :D
 

Reply to Two Ovens, One Cable in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I'm about to replace our kitchen and one of the upgrades is to install two full size ovens to replace the original twin over under...
Replies
7
Views
1K
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
Hi all, I've recently had an oven installed by AO and afterwards I noticed in the installation instructions that the electrical connection needed...
Replies
1
Views
1K
i am looking for some help with a decision i need to make. i am having a new kitchen installed but can decide between having 2 3.6kw 16amp ovens...
Replies
4
Views
855
Hi, we are replacing our old hob and cooker and I need a bit of help, to make sure all is safe. This is the oven and hob specs: AEG IKB64401FB...
Replies
0
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock